FUnction Block for finding the second highest value
mthompson6782
Mar 2014
houton
I am trying to find a function block to determine the second highest value ( i need the second highest value out of 16 thermocouple temperatures) in a Triconex PLC. Does anyone have a canned version of this they would like to share?
why don't you think about the problem and suggest your solution then someone may help you
Declare Highest /2nd Highest
If IN1 > IN2 then
Highest=IN1
2nd Highest =IN2
end if
etc
No need to sort into order, e.g
Code:
FUNCTION_BLOCK FB97
VAR_INPUT
T:ARRAY[1..16] OF REAL;
END_VAR
VAR_OUTPUT
SecondHighest:REAL;
END_VAR
VAR
i,j:INT;
END_VAR
BEGIN
j:=1;
//find highest and make it very low
FOR i:=1 TO 16 DO
 IF T[i] >= T[j] THEN j:=i; END_IF;
END_FOR;
T[j]:=-99999.0;
//find highest again, this will be the second highest
j:=1;
FOR i:=1 TO 16 DO
END_FOR;
SecondHighest:=T[j];
END_FUNCTION_BLOCK
Code:
FUNCTION_BLOCK FB97
VAR_INPUT
END_VAR
VAR_OUTPUT
SecondHighest:REAL;
END_VAR
VAR
i,j:INT;
END_VAR
BEGIN
j:=1;
FOR i:=1 TO 16 DO
END_FOR;
T[j]:=-99999.0;
j:=1;
FOR i:=1 TO 16 DO
END_FOR;
END_FUNCTION_BLOCK
I really appreciate your response. I think this is exactly what I was trying to do. I have been fiddling around with this and have decided that using structured text is the way to go. I was able to find the second highest using all function blocks but the method i used had problems when the second highest value was the same as the first.
Using function blocks I used the MAX of the 16 inputs then subtracted the max from the original tag values if the value was Not EQUAL to zero it outputted a 1 which I then multiplied again by the original tag values and sent to a MAX block which yielded the second highest. My way is bulky, labor intensive, and clumsy.
I want it so that if the second highest value is equal to the highest value it displays that value twice.
I have read that ST is very much like PASCAL and I have decided to try to sharpen my ST programming skills in this area. Thank you very much.
Hi, I have attached herewith one image which our programmer has been used in S7 1500 PLC. Now we need to use the same instructions in S7 1200 PLC...
143
Please see attached file. I need this program in Function Block form but I am totally lost on this. Any help would be appreciated. Thanks!
330
Hi! I am using a TM200CE40T PLC from Schneider to write data over Modbus. I have used Memory words (%MW) before using the Write variable...
553
Hi folks. New to the forum, but been working with PLCs for several years now. Would like some advice on whether you would keep this logic, or...
1,086
Hi Yes, I'm stuck again. Trying to define a Function Block. What I've put in there so far has been a straight copy/paste from the code (and that...
22
3,004