general dc input question
I take your question to mean, 'Is a discrete input pin left open interpreted as the '0' state?'
'YES' for Allen Bradley SLC, Micrologix and ControlLogix. Also AutomationDirect 05, 06, 205, 405.
That's also a yes for Siemens (S5, S7-200, S7-300/400), Omron CQM1, Mitsubishi FX and Philips PLC10 and PC20 (now Nyquist, I believe). In fact, I haven't seen any other situation so far and I've been active in this field of expertise for over 28 years now.
Kind regards,
I cannot remember a PLC that I have used in the last 25 years that treated a discreet input pin left open differently quite frankly - have not used everything available of course but have used plenty.
If you read the specs on the input cards it will tell you the threshold of the input voltage e.g. < 8.5v is logic 0 > 16.4v is logic 1 (these figures are not actual ones taken from input cards as these will vary from manufacturer).
PLC's are not like logic chips that can have a tri state
What is your perspective? Are you a Maintenance Tech? Systems Integrator? OEM Engineer? What are your thoughts on the topic of source...
24
1,178
Wizards, It has been a few, but you all have always done me well. I have acquired a 1769-L33ER and want to use it as my collection PLC to...
535
Hi! I recently discovered how to get to configuration mode and disable printing for connecting to PanelBuilder32 and updating my Panelview...
454
Hello Guys, Hope everyone is doing well. I have a general doubt about ladder programming. The outputs are not getting energized when I used the...
1,888
Hey all, I'm teaching myself PLC programming, and don't have a lot of resources at my disposal, so probably a very basic question, but I recently...
2,433