Hi Guys,
Not really sure I get your point, I think we have one of those cant see the Forest because all the Trees are in the way scenarios going here.
So lets recap:
My post was about using a cable that has a SHEILD surounding a conductor. (Only a shield, not a seperate shield and a seperate ground wire) The cable assembly is listed as having only a shield in the spec sheet, no where does it mention anything about Ground/PE/Earth condutor.
QUOTE FROM SPEC:
"OLFLEX FD 90 CY with tinned copper braid SHIELDING is used for applications where EMI emissions need to be suppressed"
I have an engineer telling me that it is ok to use this SHIELDING as a ground conductor. (Nowhere in my cable spec does it say that this SHIELDING is meant as or rated for this purpose.)
I think this is pretty cut and dry and no one can say otherwise. Would you not aggree?
Then you post the Draka cable MCMK. This cable has the GROUND conductor spread around the outer circumference of the cable assembly.
So now we know that Draka's GROUND conductor configuration is unlike most other cables. They have it wrapped around the votage conductors instead of being a seperate single conductor the way we normally see the GROUND conductor in other cable assemblies.
Thats fine it is still a GROUND conductor, it is approved and listed as such, as PE, it says so right in the spec for the cable.
However no where for the MCMK cable assembly does it say anything about this cable being compatable for the suppression of EMI. (I have looked and I see nothing, if it is there please point it out)
Then you post another cable that is supposedly proving your point that the shieling on a cable assembly can be used as a ground conductor.
I dont see it that way, BECAUSE the MCCMK cable assembly you posted now has a seperate foil SHIELDING that is used to suppress EMI and a seperate GROUND conductor that just so happens to be wrapped around the foil shield, only because this is the configuration Draka has chosen for there GROUND conductor.
Here is the link to Prysmian Group that you keep refering to.
http://www.drakakeila.ee/index.php?group_id=29&page=69&
I do see a few cables on here that are rated as Electro Magnetic Compatible Cables, as is the MCCMK cable you referance. The MCMK that you first posted says nothing about being Electro Magnetic Compatible. (This is because it is missing the seperate foil SHIELD)
Whats your point?
All cable manufactures offer cables that are Elecro Magnetic Compatiable.
They are called SHIELDED cables.
They have a SHIELD that is used for the suppression of EMI and they have a SEPERATE GROUND conductor for grounding the equipment and as a path for fault currents.
The MCCMK cable you show is no different than any of the other cable manufactures SHIELDED cables. It has a seperate foil SHIELD and a seperate GROUND conductor.
The only differance is Draka has chosen to configure there GROUND conductor in the cable assembly different from most cable manufacturers.
I think this is obvious, as you can see Draka has the same GROUND conductor configuration in there NON-SHIELDED cables as they do in thier SHIELDED cable assemblys.
I see the forest quite well, the trees are the forest. Take a few steps back and have a good look, can you see the forest?
Dont know about you but I am bored with the subject.
Dont get me wrong, I enjoy the back and forth exchange of ideas and difference of opinions, its what keeps us sharp and most times I learn a thing or two from it.
But we have whipped this poor horse to death, and I think we should put it out to pasture.
Have a great day and look forward to chatting with you around the forum. (Only in another thread on another subject)
Best Regards,
BCS
Not really sure I get your point, I think we have one of those cant see the Forest because all the Trees are in the way scenarios going here.
So lets recap:
My post was about using a cable that has a SHEILD surounding a conductor. (Only a shield, not a seperate shield and a seperate ground wire) The cable assembly is listed as having only a shield in the spec sheet, no where does it mention anything about Ground/PE/Earth condutor.
QUOTE FROM SPEC:
"OLFLEX FD 90 CY with tinned copper braid SHIELDING is used for applications where EMI emissions need to be suppressed"
I have an engineer telling me that it is ok to use this SHIELDING as a ground conductor. (Nowhere in my cable spec does it say that this SHIELDING is meant as or rated for this purpose.)
I think this is pretty cut and dry and no one can say otherwise. Would you not aggree?
Then you post the Draka cable MCMK. This cable has the GROUND conductor spread around the outer circumference of the cable assembly.
So now we know that Draka's GROUND conductor configuration is unlike most other cables. They have it wrapped around the votage conductors instead of being a seperate single conductor the way we normally see the GROUND conductor in other cable assemblies.
Thats fine it is still a GROUND conductor, it is approved and listed as such, as PE, it says so right in the spec for the cable.
However no where for the MCMK cable assembly does it say anything about this cable being compatable for the suppression of EMI. (I have looked and I see nothing, if it is there please point it out)
Then you post another cable that is supposedly proving your point that the shieling on a cable assembly can be used as a ground conductor.
I dont see it that way, BECAUSE the MCCMK cable assembly you posted now has a seperate foil SHIELDING that is used to suppress EMI and a seperate GROUND conductor that just so happens to be wrapped around the foil shield, only because this is the configuration Draka has chosen for there GROUND conductor.
Here is the link to Prysmian Group that you keep refering to.
http://www.drakakeila.ee/index.php?group_id=29&page=69&
I do see a few cables on here that are rated as Electro Magnetic Compatible Cables, as is the MCCMK cable you referance. The MCMK that you first posted says nothing about being Electro Magnetic Compatible. (This is because it is missing the seperate foil SHIELD)
Whats your point?
All cable manufactures offer cables that are Elecro Magnetic Compatiable.
They are called SHIELDED cables.
They have a SHIELD that is used for the suppression of EMI and they have a SEPERATE GROUND conductor for grounding the equipment and as a path for fault currents.
The MCCMK cable you show is no different than any of the other cable manufactures SHIELDED cables. It has a seperate foil SHIELD and a seperate GROUND conductor.
The only differance is Draka has chosen to configure there GROUND conductor in the cable assembly different from most cable manufacturers.
I think this is obvious, as you can see Draka has the same GROUND conductor configuration in there NON-SHIELDED cables as they do in thier SHIELDED cable assemblys.
I see the forest quite well, the trees are the forest. Take a few steps back and have a good look, can you see the forest?
Dont know about you but I am bored with the subject.
Dont get me wrong, I enjoy the back and forth exchange of ideas and difference of opinions, its what keeps us sharp and most times I learn a thing or two from it.
But we have whipped this poor horse to death, and I think we should put it out to pasture.
Have a great day and look forward to chatting with you around the forum. (Only in another thread on another subject)
Best Regards,
BCS