I am facing one problem on each download one of the point just get in fault and error is resource unavailable.
I have 2 racks of point and same goes for both on each dowbload random module get faulty.At the moment, I am keeping one module as inhibit.
PLC : Guardlogix l81es
Chassis size : 11
Aentr-DI-DI-DI-Di-DI-24VDC-DI-DI-DI-DO-DO
Aentr:DO-DO-DO-DO-DO-24VDC-DO-DO-DO-DO-DO
DI:IB8S
DO:OB8S
I ran into this a few years back.
The AENTR can only have 20 CIP connections, if safety modules are used.
By my count, you are at 21 connections with default settings.
https://rockwellautomation.custhelp.com/app/answers/detail/a_id/34984
Access Level: TechConnect
Basically, it means reducing the connections in each rack.
I had to change the connection type to none in the module definition of the AENTR.
This only works if there are no standard digital I/O modules.
I also had to disable the test output data in the IB8S module definitions on a few modules where I didn't need test outputs.
Reference manual: pages 79,
https://literature.rockwellautomation.com/idc/groups/literature/documents/um/1734-um013_-en-p.pdf
Each safety module takes up 2 connections with default settings.
The AENTR takes 1 connection, as well.
Hi Gents, I am battling for a few days now an issue at one of my customer's site with a Guardlogix system. The System has the CPU's and three...
8,833
gents, I am trying to configure communication with EMERSON PK300 controller through port A1 using generic ethernet communication module . I could...
114
I had a comms fault between my VFD and Controller (5069-L320ERS2) that started about a month ago and happened maybe once a day to now where it...
291
I just finished a project that was using a CompactLogix(5069-L310ER2)and the project now requires a GuardLogix(5069-L310ERS2). I will be...
628
I have a GuardLogix PLC with safety inputs of HMI, Estops, Light Curtains, and Gates. Is it considered safe for the safety program to monitor the...
788