HART over 1794-IE8H
subjwd
Oct 2004
18
I have a 1794_IE8H Flex I/O module with some Rosemount 3102 Level Transmitters connected. However, I can't see any HART data. Is there something I need to do to enable HART on this module? And if so, how?
I have these same transmitters connected to a 1769sc-IF4IH/A module on a 1769-L35E CompactLogix and I see the Hart data with no issues. However, on the 1769sc-IF4IH/A module the are "Enable Hart Communication" checkboxes for each channel. I don't see anything like that for the 1794-IE8H. The 1794-IE8H is connected to the 1769-L35E PLC via a 1794-AENT module.
Thanks in advance.
Check input range, default is 0 to 20ma. It must be 4 to 20ma. (see picture below)
I have not added a 250 ohm resistor. I'm no longer onsite and I'm trying to troubleshoot remotely. The transmitters are wired as shown in the manual - I think the module takes care of the 250 ohm resistance. I do not have resistors on the 1769-IF4H/A module, but those read fine.
The channels are all set of 4-20mA and I'm reading values. The filter is also set for 2sec (0.5Hz). Any other ideas?
Somebody knows something about this problem
I have the same problem, when i try to send a hart command sometimes works ok, but sometimes no, and the controller only sends zeros for de values that i need, anybody fix this problem?
Long shot:
Somewhere in the manual it says that the Flex I/O module acts as a HART multiplexer.
Other HART muxes use addresses from 1 to X for each HART device, none use HART address zero.
4-20mA conventional HART (without a mux) uses address zero, and that works fine, for multiple devices to all be address zero because a handheld is point-to-point communications with a single HART device.
Could the Flex I/O module be assigning HART addresses (above zero) to each device ?
A handheld will fail to communicate if the address is incorrect.
The handhelds have an address selection for dealing with non-zero addresses.
https://literature.rockwellautomation.com/idc/groups/literature/documents/um/1794-um063_-en-p.pdf Hello. Trying to figure out if it would be...
1,812
This is going to be long winded just because i am going to try and provide as much info as possible. Over the last month i have had the...
2,426
Dear all, I have 1794 IE8H Hart flex input module to which one Emerson HART flowmeter is connected...I have gone manual of flex module...I have...
20
8,836
Good day gentlemen. I've run into a problem with AB 1794-IF8IH Hart Analog input module. The problem is that i'm able to see analog input...
2,356
Good Morning , I am looking to modify a machine , and I am looking at using Rockwell Automation Flex I/O modules . I ne a few analog output...
2,574