heat control with PLC
hapetter
Feb 2009
Kristiansand
58
Hi.
I like to do heat control in a house with a PLC. I want to control a termostat lets say for flor heat. I want to set power/temperature setpoint and read temperature to/from PLC.
In general I want similar functionality as EIB/KNX but it is to expensive and I try to do it without this system.
Any suggestion to a termostat og a way of doing this with a PLC? I use Beckhoff PLC and I/O components.
Thanks!
Best Regards
Hans Pettersson
Sounds like a good project.
I'm not sure what EIB/KNX is but have a think about this.
You need: 1) Something to measure temperature - Thermocouple / RTD to an analogue input 2) Something to set the temperature - HMI / Potentiometer / BCD switches 3) Something to control power to the heaters - SCR.
Program a PID loop with set temperature and act temperature as inputs and a 0-100% output. Take this output value and use it to control the SCR; e.g. if the output is 80% the SCR is on for 4 seconds out of 5, 20% = 1 second out of 5 etc. (Siemens S7 have ready made block to do this - FB43).
Other features that you may wish to considder are: Different setpoints for different times of day? Measure outside temperature to estimate heat loss and pedict power required?
Just some thoughts
Nick
Is there anyone to explain all details of Siemens S7 PID programming? I have Siemens documents but it is really difficult to understand, I believe that there is different method to use it more effective then copy/past from another project..
Thanks in advance..
I've always thought the the documentation for FB41 was very good. have you tried to highlight it in your project and press F1?
The parameter assignment and monitoring tool is also very useful with its real time trend of setpoint, feedback and PID output. This is really useful for monitoring heating loops for Ziegler Nichols analysis etc.
Edit: If you don't like the Siemens blocks or they don't do quite what you wanted, you can always write your own.
Nick
Hello everyone. I've been away for quite awhile... My questions is more logic based than PLC programming per say. I'm using a Do-more processor...
6,345
Dear, i am looking at the control of heat exchangers. I have one set of two heat exchangers. When i select its control valve that will be...
2,514
I am trying to build ladder logic in rsl5k to turn on a contactor with a digital output. I have a 1769-IT6 input card and a 1769-OA16 output card...
1,952
Hi all, Looking for some basic information on the control of a heat exchanger via a PLC. I am using the Siemens S7-200 PLC... Its the first...
2,777
Hello all! I am fairly new to the world of PLC's and this forum, so I apologize for my lack of knowledge. I have a Powerflex 753 that keeps...
570