HELP RED LION Graphite won't start
ERCfarcontrol
Apr 2015
Fresno, Ca
63
I'm working on a Graphite that is continuously looping through the start up sequence then stops and shows a page that says "system could not start" "touch left to clear, touch right to retry"
This happened after I uploaded a change. When I uploaded, it also automatically updated the firmware.
I'm currently up a creek. HELP!
No backups.
The same thing just happened to me on another touch screen that I just started building. It is a very small configuration.
Will uninstalling crimson and reinstalling a previous revision set the firmware back?
I doubt you need to downgrade firmware, although that might help temporarily. It is likely that the database got corrupted. Load a known valid database image on a the root of a memory card and name it image.ci3
In Crimson software, from the file menu choose File > Save Image, and then it will create a complete image, firmware and all. That is the surest way to recover from an endless reboot cycle. The alternative is to catch the unit when first powering up and click the send button in Crimson (use a USB connection). If your timing is slightly off, try again (power cycle, click send just after the logo screen appears).
Using a valid image.ci3 file on a memory card eliminates the need for perfectly timing the download attempt.
I have done this apx. 3 times in ten years and was always able to recover with one of these methods. One time I had an uh-oh in a program I was calling on startup. One time I had a corrupted database that I fixed by starting a 2nd instance of Crimson and dragging the important and known good parts from the corrupted file into.
I forget the 3rd occurrence, but was something similar.
They must have added it since it's happened to you, but it retries to start the configuration 3 times before it stops itself and displays a page that gives you the option to clear the configuration or retry again. Hit clear and you can start from scratch again, no looping.
I uninstalled crimson, reinstalled older revision, saved my file as older rev, no luck. I have made modifications using the latest rev prior to this instance and had no issues. I must have corrupted something somewhere along the line. I can load a blank or my last known and it starts up just fine. I do have a program called upon on startup. The other configuration that is doing the same thing is quite small, I'll check out it's similarities.
I figured out what was causing the start up issue. I had minimum and maximum tag limits directing toward each other with addition and subtraction. I attached a couple screenshots, maybe I can get some insight as to why this caused the issue.
The tags are On and Off setpoints for starting and stopping based on pressure. The idea behind it was to keep the on setpoint below the off setpoint and the off setpoint above the on setpoint. Am I not entering the expression correctly? Is it because I'm referring the tags in a circle? How would one go about making this possible at the hmi level and not the PLC.
I tried creating 2 new general expression tags with the off/on sp arithmetic (that is correctly calculating) and directing those tags for max and min entry limits. It still causes the loop.
To get it right I created 2 programs that run on data box select. They perform the + or - arithmetic and places the result into my entry limit tags. Works great.
So, the problem was continuously directing the min and max entry limits of 2 tags to each other:
--"hi" tag minimum entry directed to "lo" tag value
--"lo" tag maximum entry directed to "hi" tag value
Thanks everyone. Good to know that saving a file with an earlier software revision will also change firmware of device back.
Hello, We are currently running a bunch of g310's connected to their SLC5 PLCs through ethernet. I've attempted to upgrade the program from 2.0...
1,126
Hey guys, I was wondering if a G303 Red Lion HMI can be used as a scanner? I am having trouble finding information on this. Thanks
1,409
When you are compiling (translating in Red Lion parlance) user defined programs - what does "Unexpected End-of-Text" error mean? It is at the END...
1,801
Hello everyone, Brian the Newb here again regarding Crimson 3.0 and J1939 CAN protocols. I had searched the archives and I DID find a couple of...
3,001
I have a cardboard baler that uses the Red Lion CL05 interface to control bale size, wire twists and a couple other things. It is showing invalid...
2,816