Hi Guys
i am a bit confussed? i am looking at adding a 1734-oe2v module to a point i/o unit to control the speed of a powerflex 40, how do i set up the module engining valve / what is the eng value ment to be ?
i have set the pf40 to 0-10v speed ref?
i hope somebody can help with my thoughts thanks stu
Hi Guys
I haven't used this module, but it is a Voltage Output Module, so you will have to use 0-10V if you only need Unidirectional Control. I think you will find the information you need in these manuals.
Installation Instructions:
http://literature.rockwellautomation.com/idc/groups/literature/documents/in/1734-in002_-en-e.pdf
I/O Module Manual:
http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1734-um001_-en-p.pdf
Stu....
The newer Analog Input and Output Modules from Allen Bradley allow you to do the scaling in them. Therefore, you don't need to do the Scaling in the PLC Code. In the example you posted, if you write 0 to the module you will get 0 Volts out, if you write 750 to it, you will get 10 Volts out, and if you write 375 to it, you will get 5 Volts out.
You need to set the Engineering Units to match the PLC Code that is driving it, or visa/versa. For example, if you had PID Instruction controlling a process via a control Valve. In the PID instruction you Scaled the Output (CV) to 0-1000. You would set the Module Engineering Units to match.
Stu......
HI everyone, i am new to Siemens plc programming and i am in need of some help. yesterday we had an S7-1200 CPU 1214C fail to turn on an output to...
161
I have an old Sentry Palletizer (S/O Number 3007 / Serial Number 1172) that has lost its program as the backup battery died years ago. I can...
106
Hello, I need to write the following program in Ladder language, but I could not integrate the Fibonacci sequence into the ladder. Can you help...
22
475
this a program to send data to barcode printer I want to integrate a new printer in a new machine and i wanted to adapt the old prgram on it but I...
177
68