I need help determining how to code a motor FLA reading. The HMI has a numeric display with a bar from 0-150% FLA and it's looking for a integer number in a SLC 500 processor.
I have the Motor data plate FLA in a integer data file and I have the actual FLA of the motor from the current ring in a float but how would you code that to compare to the data plate FLA and display a integer number 0-150?
If the actual amps is greater than the FLA, you will be over 100%. There is no need for any other scaling. If your motor should exceed 150% it will simply peg the bar, the numeric will still be accurate. In the real world, this condition won't last long, the motor will trip on overload.
I tried a compute block online where I have F60:0/F60:1*100 with a destination of F60:2 and F60:0 is my actual amps and F60:1 is my data plate FLA but the compute block won't accept and says it has errors?
I tried to make the destination a integer file also N100:0 but it won't accept that either?
Where am I going wrong?
Hello everyone. Could someone please assist me? I am using Citect version 7.2 service pack 5 and Windows 7. I have created a project...
93
Hello, I'm not sure if anyone can help me. I made a big mistake by pulling out the battery to swap it with the machine turned off, and as a...
63
I've adjusted the IP of the Panelview Plus as well as the DNS servers; the screen does not show up in the search when I go to the transfer utility...
196
Hi Everyone, I own a GE Versamax controller that I purchased for a class at Long Beach City College a couple of years ago. I lost the use of my...
332
I was wondering if anyone could help i am trying to use a SLC 500 with a 5/05 processor to set up an incremental encoder to a HSCE2 card? The card...
193