chavak
Member
- Join Date
- Jul 2002
- Posts
- 751
You are using L71, so I'm assuming you have a PV plus as a HMI, then
Create 2 tags in the PLC,
Dint tag type, name it PB
Bool array with data size of 128, name it A[128]
On the HMI create an Interlocked Push button with a tag of PB, copy and paste it 128 times, and edit the button values 0 thru 127
On the HMI create 128 multistate rectangular indicator with 2 states for values 0 and 1, with a tag address from A[0] thru A[127]
At the PLC add an unconditional rung with OTE with a tag element as A[PB]
Create 2 tags in the PLC,
Dint tag type, name it PB
Bool array with data size of 128, name it A[128]
On the HMI create an Interlocked Push button with a tag of PB, copy and paste it 128 times, and edit the button values 0 thru 127
On the HMI create 128 multistate rectangular indicator with 2 states for values 0 and 1, with a tag address from A[0] thru A[127]
At the PLC add an unconditional rung with OTE with a tag element as A[PB]