I have an input card analog. I need to compare it value to a number. I try > but it does not like my comparison I guess.
Do I move this value to a DM first.
By the way...DM I am guessing its just a Omron way of saying memory location that I can use. How may are there and whats there values ?
Also what exactly is
CIO W H A T E E? ETC....
THANKS
MARK
It is perfectly legitimate to compare the input value from the analog card directly to either a constant or another memory location such as a DM (Data Memory.) Please give more information about the way that you constructed your comparison.
Do I move this value to a DM first? By the way...DM I am guessing its just a Omron way of saying memory location that I can use. How may are there and whats there values ?
DM (Data Memory) is a data-retentive (battery-backed) memory area which is used primarily as a place to hold either a Hex or BCD numeric value. DM's can be set either by moving a constant value to them in ladder or by pre-setting them using the Memory Component of CX Programmer. Once a Data memory is loaded with a value, that value will be retained even during a power cycle.
The number of Data Memories is dependent on the Omron PLC model. You haven't told us what Omron PLC model that you have.
CIO (Core I/O) is the area of memory where the input and output structure is addressed. It includes local I/O, remote I/O, intelligent and special I/O. If an CIO address is not used then it is available as an internal memory location.
And about now I expect BobB to chime in and tell us about the contiguous memory mapping of the Omron memory structure. Bob?
Hello thanks
Processor CG1G-H-CPU44
In the compare (>) do I need to mark or tag the front of the CIO with something for it to relize that is what I am looking at.
My analog is at 2000.4 do I need to label it in the greater than, like
CIO:2000.4 or should 2000.4 be good enough. Also the number I compare it to does it need to be in a certian format, Decimal, Hex, ???
thanks
Mark
Hello again
the error I get is
ERROR: Operand 1 Memory area not valid at rung 25 ( 0, 1 ).
It seems like the processor does not like > or = or any compare
I would guess that your analog value is not 2000.04 (which is a bit designation) but is 2004 (which is a word designation). The CIO memory area is the only area which is not preceded by a prefix. Therefore your word is simply 2004, not CIO2004. What is the model number of the analog card?
Regarding the number for your comparison, it depends on whether you are using a analog card which does its' own scaling. If so, it will be BCD. If not, it will be HEX. Either way, the number needs to be preceded by a "#",which denotes a constant.
2004
#1234
Hello
the analog card is a cs1w-iaaaa
Its a 9 in 1 out analong card in a rack.
How would I tell the plc to look at the 4th input value
thanks
How would I tell the plc to look at the 4th input value?
If the unit number of the module is 0, then the 4th input is word 2004.
RTM:
http://forum.mrplc.com/index.php?act=Downloads&CODE=02&id=63
We have an omron CJ2M-CPU12 PLC that we are having issues with an AD04U analog card. it is connected to a K type thermocouple sensor. The card is...
611
Hi all, While i am not new to omron, i'm totally new to the analog part and lost. i have a CJ2M cpu 33. then there are 4 i/o cards card 5 is a...
26
2,613
Hi all, I only do PLC Programming on and off and have never done programming analog stuff therefor I need a pointer in the right direction. We...
4,616
I have a question about SET instruction in Cx-programmer. When condition goes true it is supposed to give value 1. But, my controller is giving 0...
24
2,308
Our small company ran into a huge problem... the battery in our Aqueous wash PLC exploded, and destroyed the PLC and Program along with it. We...
42
11,999