I have 3 temeprature, where I need to know which is the highest. It should be moved to a register. How do I do it most easily. It should work both, when the temperature rises and falls
Rslogix 500
Make yourself the plc. In this case, how you would do it is the way you should tell the plc to do it.
Assume you are sitting at your desk. You can't remember ANYTHING for more than 1 second but you have a pencil and a pad of paper. Someone walks by your desk and and drops off three slips of paper, each with a number on it. You are allowed to look at each slips only once and you can't remember what they are once you look at them. How would you decide which is the highest?
Keith
Hojland:
Three temps, a,b and c.
For high temp: If a>b and a>c or b>a and b>c, or c>a and c>b. The one that is true must be save to a buffer.
The same analysis for low temp but <.
Then repeat same procedure every time you need it.
william
First, assume A is the "winner" value or "high score" register. I will call it H. (Let H=A).
Then compare the others to H one by one and MOVe any greater value into the "winning" register.
------------------+-MOV----------+
|Source I:1.0|
|Dest N7:0|
--+-GRT-----+-----+-MOV----------+
|A I:1.1| |Source I:1.1|
|B N7:0| |Dest N7:0|
|A I:1.2| |Source I:1.2|
|B N7:0| |Dest N7:0|
I am using a A?B 5/04 with RSLogix 500 and I am trying to come up with a way to display the highest temp from one thermocouple in a 24 hour...
1,791
folks i have 104 lamps that record their hours on the panelview, so i need to get the highest hour value of these lamps data data type is...
26
5,551
Hello Currently have a project in which I have to find the highest value in a dint array. Once the highest value is found I will have to move...
20
11,551
This is a Citect SCADA question I have Six variables of type REAL (Float) to compare and determine (identify) which variable has the highest...
1,433
Hey. (AB CLX) I have an application where I am recording faults into an array of 15 DINTS. The Members of the array represent different faults...
1,435