hmi and plcsim

seee

Member
Join Date
Dec 2010
Location
singapor
Posts
112
hello.
Is it possible to connect easy view hmi software
to plcsim in order to simulate both hmi and S7 plc program?
best regards.
 
thanks a lot for your reply.
but what should i do in easy view software?
(i do whatever you had told in the pdf file)
could you please give me an example?
thanks.
 
I don't know the easy view hmi software.

But in general there should be an option where you can configure the IP address of your plc, and for S7 rack and slot number.

Example:
Your PC where Plcsim and Nettoplcsim is running has the IP address 192.168.1.10.
Then you have to configure this IP in your hmi software. Both devices should be in the same subnet, for example 192.168.1.20.
First step is a simple ping test between both partners.

Just think of, your PC where Plcsim is running is your real plc.
 

Similar Topics

hi everyone. i hope you guys are doing great. i am trying to built communication between aveva intouch hmi 2023 and tia portal v18. i dont have...
Replies
1
Views
628
I have a cell with a compact guardlogix as the plc and I have three hmi's and two vfd's on this cell. I been experiencing momentary comms faults...
Replies
10
Views
111
What is the best way to show a modules LED status lights on an HMI screen? The module I'm trying to mimic is the 1756-DNB DeviceNet Scanner...
Replies
0
Views
51
I'm having a hard time either remembering or figuring this out. I have a PLC program and the associated HMI program. I know what this means...
Replies
4
Views
118
Hello, I'm working with Studio 5000 and ME Station, and I'm trying to find a way to detect if the PC with the HMI is shut down or not. I've tried...
Replies
6
Views
191
Back
Top Bottom