HMI versus OIT
HMI = Human Machine Interface
OIT = Operator Interface Terminal
You may also see MMI - Man Machine Interface. Now considered politically incorrect so you don't see that as often.
All referring to an Operator Screen
Some projects will define OIT as the local interface for a controller. The HMI is the plant level, or SCADA interface for multiple controllers or the system as a whole.
Other projects do not specify a difference. Check the specs.
Perhaps OIT's are smarter today. Years ago, the OIT didn't have any smarts. Much like a dumb terminal. HyperTerminal, for example, except these just have 2 or 4 line LCDs.
Set up RS232, and send it text. Read key presses.
All of the processing is done inside the PLC. Send ASCII text. Read ASCII characters coming back. An absolute pain to program and test.
An HMI is a single board fanless PC. It has a built-in software, most likely running Linux.
You use a program to set up everything, and write it to the flash memory in the HMI. The PLC reads and writes registers in the background. This is all automatic, based on your address table. The only thing you need to set up is the baud rate and protocol. Modbus, for example.
Small HMI's are so cheap today, I can't justify an OIT.
For me, the difference is easy - OIT's are obsolete.
A trip down memory lane ...
I still chuckle at A-B changing they're terminology from MMI to HIM years ago. Human Interface Module on the old 1305 drives
I have an application where I am currently reading very small amounts of data from as many as 15 processors using a ML1100 dedicated to that...
5,920
I have a cell with a compact guardlogix as the plc and I have three hmi's and two vfd's on this cell. I been experiencing momentary comms faults...
150
What is the best way to show a modules LED status lights on an HMI screen? The module I'm trying to mimic is the 1756-DNB DeviceNet Scanner...
59
I'm having a hard time either remembering or figuring this out. I have a PLC program and the associated HMI program. I know what this means...
118
Hello, I'm working with Studio 5000 and ME Station, and I'm trying to find a way to detect if the PC with the HMI is shut down or not. I've tried...
213