How to connect iFIX to an SLC500 PLC?

ruby.n

Member
Join Date
Dec 2009
Location
USA
Posts
48
Hi have iFIX installed on my machine. I have an IGS driver configuration file. How do I get iFIX to talk to my PLC? I also have RSLinx installed...
 
Use OPC. If your iFIX has an OPC Client already, then install this OPC Server for your SLC500 and then connect your iFIX to the OPC Server:
http://www.matrikonopc.com/opc-drivers/opc-Allen-Bradley/base-driver-details.aspx

If your iFIX doesn't have an OPC client built in, then install this OPC server and the one above:
http://matrikonopc.com/opc-drivers/1693/index.aspx
configure them both and then use OPC Data Manager to connect both OPC Servers together and get data moving between your HMI and PLC.
http://matrikonopc.com/products/opc-data-management/opc-data-manager.aspx

Let me know if you need any help

Wassim Daoud
Global Solutions Architect
www.MatrikonOPC.com
 
Last edited:
Hi there...

I had installed an ABR7 driver, but it came up with an error 'API not initialized'

So I have now switched to using an IGS driver...

Thanks so much though...
 
If you have installed the IGS driver (And have the IGS driver option in your license key). what is your question ?

Do you want to know how to configure a iFIX Driver ?
 

Similar Topics

I had to install a Historian v6.0 IFIX collector on a 32-bit machine, because the v7.0 collector kept failing on install, despite the manuals...
Replies
0
Views
1,797
Hello All, I am wondering if anyone knows if it is possible to connect iFIX to an OPC server (IGS) running on another machine. In the SCADA...
Replies
1
Views
1,537
Greetings, I had an issue with a RIO rack 2 and IFM I/O Link dropping on my network. I would loose connection for a second or 2 then they would...
Replies
3
Views
105
Hi friends, i need a help to know the procedure and steps to connect Lenze i700 to PC for parameterize. i tried with lenze easy-starter using LAN...
Replies
0
Views
59
Hi, We have been facing a issue with SCADAPack 474. Configuration is like below. RTU 474 + 6103 PS + 5606 IO Mix Module + 5414 DI Module Only...
Replies
0
Views
82
Back
Top Bottom