thehoneybadger
Member
LOL. Hey bitboy. Not quite what i meant.Good point, the transducer should should be level with or below the pump suction, with a way for air and/or vapor in the tap to rise or purge to ensure the tap is full of liquid only.
But OP is going with float switches, so this analogue approach, which would bypass and solve the problem with the WIKA breather, is moot.
I meant in the drawing, the vertical line is like the only straight line in the entire drawing. Which is why it was out of place. (Just a little comedy relief)