osmanmom Member O Join Date Mar 2014 Location JOHOR Posts 1,457 Sep 29, 2014 #31 your reference link.
AdamG8GXP Member OP A Join Date Jun 2011 Location Chicago, IL Posts 35 Sep 29, 2014 #32 JesperMP said: Are you using STEP7 v5.x or v1x.x ? WinCC Flexible or WinCC v1x.x ? Click to expand... I have: STep 7 V5.5 + SP1, revision level K5.5.1.0 WinCC Flexible 2008 SP2
JesperMP said: Are you using STEP7 v5.x or v1x.x ? WinCC Flexible or WinCC v1x.x ? Click to expand... I have: STep 7 V5.5 + SP1, revision level K5.5.1.0 WinCC Flexible 2008 SP2
JesperMP Lifetime Supporting Member + Moderator Join Date Feb 2003 Location ᚴᚬᛒᛅᚾᚼᚬᚠᚾ Posts 16,351 Sep 29, 2014 #33 The one called "Projects for SINAMICS G120 with CU240E-2 xx F" when you follow THIS LINK contains a KTP600 project for WinCC Flex 2008 SP2.
The one called "Projects for SINAMICS G120 with CU240E-2 xx F" when you follow THIS LINK contains a KTP600 project for WinCC Flex 2008 SP2.
seppoalanen Member Join Date Jan 2003 Location Finland Posts 1,132 Sep 30, 2014 #34 #CRW is Output type ctrl word #CONTROL.ACK_FAULT is bit 1.7 of DIW18 (in STAT) [remember Simatic byte order!] Part of FB: Last edited: Sep 30, 2014
#CRW is Output type ctrl word #CONTROL.ACK_FAULT is bit 1.7 of DIW18 (in STAT) [remember Simatic byte order!] Part of FB: