Travis,
I'm glad that worked for you. As you may already know, the 500 family SCP can let an unwanted value in!
SCP
Min In = 0
Max In=10
Min Out=10,000
Max Out= 32,767

And now the catastrophe.... analog input value of 10.1 is returned! Hello, faulted PLC!

Proceed the SCP with a LIM and your input LIMITS. That will keep Mr. SCP from going >32,769

I know it is redundant, but I've learned the hard way.
 