ifferance between s7-300 and s7-400?
Must... resist... temptation... to type... facetious reply....
"100"
....darn - I failed :)
Well, I've never been shy about expressing an opinion so I'll get my feet wet first.
A lot of money. :)
The higher-end 300 processors are essentially 400 cpu's in a 300 chassis. I have done a few single panel applications that controlled an entire process - the entire room. One was a 318 and the other was a 317 cpu (more powerful than the 318) and both had resources to spare - 20% memory left with very fast scan times. Five or ten years ago this would have required 400 power but the newer 300 line is very powerful. The 319 blows everything away - though I haven't had a chance to use it yet.
PCS7 is Siemens' answer for DCS and it does not work with the 300. The 300 processors also don't support all the interrupts like the 400's, you get an OB35 and that's it. There are other differences of course and I'm sure more people will post.
In addition to what has already been written:
S7-400 supports RIUP.
S7-400H supports hardware redundancy.
The performance of the S7-400's backplane is much higher than the S7-300. This is especially important for network connections via CPs.
Btw. The 318 was a S7-400 CPU in an S7-300 body. The 317 and 319 are real S7-300 CPUs. So they dont have the 4-level accunmlator stack of the S7-400 for example.
A lot of money. :)
S7300's will support more interrupts very soon.
We have problem in our Siemins drive SIMOVERT MV type number 6SE8001 when we look the actual speed we find it more than setpoint speed and the gap...
2,566
V
I want to know the differance between AC and DC servocontrol motors as well as Drives. Also I want a comparison with normal motors.
5,063
vnkarwa
V
I am a little new to Devicenet and I have to get a robot station up and running. The current Devicenet cables in the station are all 4 pin. The...
5,336
I’m attempt to establish a communication between two simulator M580 CPUs, using a READ_VAR, I have two vitalization Windows 10 in VMWare and each...
91
I have Woodward Controller EASYGEN-3500XT and Phoenixcontact make IO CAN-CUPLER part no: 2702230, Analog Input card: 2861412, Analog Output Card ...
47