I dont think the transducer is faulty. I had 3 of them and it is new. All 3 had the same symptoms.
I hook up to oscillopscope and measure the voltage.
at 0psi. it say 16.6v with a 2000 resistance. 1 psi it read 16.8 v. 2psi it read 16.9V. It is so strange. I really dont know what to do to make them align accordingly to linear
 
I dont think the transducer is faulty. I had 3 of them and it is new. All 3 had the same symptoms.
I hook up to oscillopscope and measure the voltage.
at 0psi. it say 16.6v with a 2000 resistance. 1 psi it read 16.8 v. 2psi it read 16.9V. It is so strange. I really dont know what to do to make them align accordingly to linear
Voltage? Who cares about the voltage as long as the mA reading is there.

I think daba nailed this one already. Your transducers are scaled differently than you think they are.

http://www.plctalk.net/qanda/showpost.php?p=441680&postcount=15
 
Put a meter in series with the transducer and verify the above.
I hook up to oscillopscope and measure the voltage.
This is your mistake. Mickey meant for you to measure the CURRENT (milliamperes) in the loop by installing a meter (with milliampere range) in "series" with the other devices already in the signal loop.
 
Hey y'all,

I got an issue with this IF-16 module, why does it only show Channels 0-7 in Offline Mode, I would like to configure Channels 8-15 as I am using the whole card for Inputs

Any input would help out...
 
When you first install the module, you must select Float Data - Single Ended mode. You may also use Integer Data - Single Endled Mode. Either way you need single ended data to see all 16 inputs.
 

Similar Topics

I've got a 4-20ma pressure transducer connected to an analog card on an AB PLC5. Under the setup for the card, I have to set a raw minimum and...
Replies
12
Views
7,432
Hi I'm trying to use a L27erm compact logix controller with high seed input I can see the pulses coming in to a counter but when I look at the...
Replies
1
Views
1,271
Hi looking to install a smaller less sophisticated PLC for fountain timing and also one analog pressure sensor which would be used to detect...
Replies
23
Views
622
Hello All, After trying to transfer some field changes on the safety scanner microscan3, and verifying, the device is stuck at .... waiting for...
Replies
0
Views
82
I have a 120V relay, 120V DI card and a analog input. I was wanting to know if i could put a 24V DI and well as a 120V DI card on the same plc...
Replies
1
Views
108
Back
Top Bottom