Instrument Wiring conections
alanyap
Jul 2014
Kuala Lumpur
72
Hey guys,
These are my concerns,
how do i know when to use the appropriate connections for these situations.
case 1:
AI card - Siemens 7kf02 - set to configuration to accept RTD
Instruments - RTD
case 2:
AI card - Siemens 7kf02 - set to configuration to accept 0-10Vdc
Instruments - potential meter with external 10Vdc Power supply.
As i know, 7kf02 can be either in sourcing mode where it can supply 24vdc to the instruments or in sinking mode.
Those wiring configurations confuses me.. any guidance??
Thanks alot!!~ appreciate it!! (y)(y)
if it is in sourcing where the input supply 24VDC means it is active input and you don't need external 24VDC in circuit. you go from + on the card to the + on instrument and - from instrument to - on card
with sinking, or passive you have to go
  1. active instrument (supplying 24VDC): + instrument to + card and - instrument to - card
  2. passive instrument: + 24VDC ext power supply to + instrument, - instrument to + card, - card to - ext power supply
Hi, this is what i've understand based on your explanation,
Please correct me, if i'm wrong....
https://www.dropbox.com/s/kcwmdnpcbtcvnj5/Wiring%20Configuration.jpg?dl=0
I always have confusion about Instrument wiring. I have to clear my concepts about so I am confident at site. What things I should know or I...
2,307
Hi all, Looking for a temperature sensing solution for determining ambient temperature in the frigid Canadian winters. Discrete outputs are fine...
1,509
I was tasked with putting together equipment for a mobile temperature monitoring system for our oil rail cars. Apparently, the crew that unloads...
841
Hello, I have a question regarding instrument cable. I know that for 4-20ma transmitters twisted pair cable should be used with the screen...
2,260
Hello, We have a 6es7 32101BL00-0AA0 DI card. There is a level switch to be added from an E&H FMR62. Our client is of the opinion that as the...
1,255