% IO reserved in PLC

sapoleon

Member
Join Date
Aug 2003
Location
salta, salta
Posts
315
Hi,
Long time not participate...
I hope that will change in the near future.

I have just one question,
How do you calculate the reserve percentage that you leave in a PLC.

the amount of free IO / used IO
or
the amount of free IO / total IO

(of each class obviously)

Thanks for your inputs.
 
Neither, just have at least 3 empty slots with at least one in the CPU rack, if rack I/O. Or the ability to add 3 nodes in a remote I/O system, preferably anywhere in the network.
If a customer wants more follow their spec and charge them for it.
Of course it is always nice to have a few I/O not used just in case somebody forgot something.
 
It depends entirely on the application.
Sometimes 10% is enough, but when there is a potential for future changes it requires much more.
The system I am doing right now has 25% spares with expansion capability of more than 5 times what is now installed.
 
example
free 25% used 75% first line means 1/3= 33%
second line is 1/4 = 25%
free space depends fully on application (i try to use 0%) as customer has to pay for something he does not get. and maybe in the future will need. and yes all systems are expandable so no need to sell bigger as needed.
 
hi,
thanks for the input.
it´s a new plant, and i´m checking the engineering.
I know is not something fixed, but... just wanted to know if there was a "normal way" of looking a it.
 
If you are the customer, then I would hope to have at least 20% spare Input and Output points. If I am the contractor or plant builder, Then I try to get about 10% spare I/O. If you have no spares at all, then revisions made during construction become very expensive for all parties.
 

Similar Topics

RX3I IC695CPU310 Prompt diagnosis of the following fault,User Memory not preserved.Another module system failure indicator light red,May I ask how...
Replies
0
Views
1,669
Hi guys, I have a couple of SLC 5/03's I need to upgrade. The installed ones are OS300 and the brand new ones are OS302. Apparently the last...
Replies
1
Views
1,909
G
I have uploaded a program from a MicroLogix 1500 LSP Series B processor. I uploaded the program while the processor is in Run Mode, therefore, I...
Replies
2
Views
10,123
HI everyone, i am new to Siemens plc programming and i am in need of some help. yesterday we had an S7-1200 CPU 1214C fail to turn on an output to...
Replies
7
Views
160
Hello, I have a Mitsubishi FX3G 14M PLC and a E615 HMI from Mitsubishi/Beijer. I'm using GXWorks 2 to do the programming and I have no problem...
Replies
4
Views
94
Back
Top Bottom