IS barriers in ESD panel
if i understand your question correctly,
IS(isolation barriers) are devices used to isolate the sensor/device from the electrical power side of the system.
you are puttting up a wall between the two worlds and only allow a small door to go between them which restricts the electrical power and return signal.
i'm not sure of your exact situation, but you are trying to prevent the raw electrical power from getting into the production side of things because of some electrical hazard or the potential of fire / explosion.
regards,
james
hi james
Thanks for your reply. i have a ESD system. I have 10 AI and 6 AO.
is it necessary to use barriers.
In my world I.S. barrier means instrinsically safe barrier, and they limit current to field devices to ensure there is not enough energy to generate a spark in hazardous environments.
And in the UK, I(ntrinsically) S(afe) circuits would typically use blue sheathed cable, terminal blocks, etc, to clearly differentiate them from non-IS circuits (which would be suitably segregated from IS).
If your existing I/O is indeed Intrinsically Safe, then any new I/O in the same field area needs to be IS (unless the zone classification has changed). As has been said, Intrinsically Safe barriers are used to provide protection to allow electrical equipment to be used in Hazardous areas - modification to such a system should not be made without a good knowledge of the area, system and protection concepts,
regards
Dave
All i understood it is necessary to use IS barriers for all type of inputs ( both analog and digital ) to limit the current in EXPLOSIVE AREAS.
regards
Dave
Yes, you need much more information and the area classification will determine what type of IS circuit devices you need.(How onerous the zone)
In this situation, I would do exactly what the designer said.
If the specifications or standards relating to the existing installation require it, then yes. It should be fairly easy to identify if the existing PLC/panel is in a 'Safe Area' or in a zoned, hazardous area. The type of enclosure is a good pointer. A hazardous area panel will be considerably larger (due to material thickness etc.) and all PB's, lamps etc. will also be rated accordingly.
If your PLC is located in a safe area, then you may be required to install IS barriers between hazardous areas and your control panel. Do you have any client specifications you need to comply with?
Rob
Thanks for All Replys
I have a ESD system in ICS triplex Trusted. panel will be installed inside control room. but instruments are in Diesel loading area. I am going to use knife edge terminals to field side connection. but i heard about IS Barriers and confused.
I have no other information from client
Intrensictly safe barriers are as stated in prior posts, I have seen them used exstensivley in vibration monitoring engine systems in class 1 div 1 areas.
Good day, could someone assist me if I'm wrong. We currently using MTL zener barriers on our current input loops. I'm measuring 17.5 vdc between...
21
5,265
Anyone ever used 1756 analog input card through a IS barrier?
1,888
Do I need to put intrinsic barriers on instruments that are rated Class Div 2 and non-incendive? The mass flow controller tech support person...
3,395
I am working on my wiring diagram for my analog outputs. I am going to use a signal conditioner/ barrier to send intrinsically safe 4-20 mA to my...
3,703
It's not a plc question but it's often comes with it... Do some of you know exactly when we need to add an intrinsec barrier in a CL1 div 2...
1,969