Is this possible with an S7 314?
sparkysliderz
Feb 2005
68
Hi Guys,
Is it possible to interrupt program flow to guarantee the capture of an event?
Am I right in saying that OB1 only takes a look at the state of inputs and outputs at the beginning of each scan?
For example. Our PLC cycles at around 13 – 17 msec’s,. does that mean that the inputs and outputs are only "mapped" 13 – 17msec’s?
If we have a retro reflective sensor on an input and the sensor only signals for much less than the scan time of OB1, will the sensor signal ever be missed?
Is there any way of guaranteeing that this event (signal) will not be missed?
Is it a 314 or 314IFM? The IFM has got 4 (I think) hardware interrupts which will do exactly as you wish. As Amr says, these can be configured to invoke OB40, where you can react to the sensor.
If it's the 314, then I'm not too sure. Sorry.
Pp
You could feed your sensor into a high speed counter card (e.g. ET200S) and then monitor the count in OB1. When the count increases, you know the input has changed from 0 to 1 for example.
It is definitely possible with an S7-314, but then you'll need an input card with interupt possibilities, the 6ES7 321-7BH01-0AB0.
Kind regards,
Hello! I need to know how fast pulse I can get (without any special cards etc.) out of my Siemens 314-1AE02-0AB0? I think the SFB43 is not...
2,106
Hello All, I need the ability to remotely reboot a Red Lion CR3000 HMI. Due to some graphics issues when the database is updated the HMI must be...
221
Hello The plant is running and there is no shutdown nowadays therefore I can add 1734- AENTR and its card while PLC is in Run? I do not wanna...
350
Folks, I have a client with an old ABB Advant / MOD300 system (v14.4). Around y2k I installed the ABB Industrial IT MOD300 OPC Server 1.1/2...
185
Hi all so i have a robot project im working on were i need to set the layers. using the hmi screen i would like to use the numeric data display to...
826