Kinetix 350 EOL is Dec 2022 - Any issues to change to Kinetix 5300?
lunenburger
Jul 2008
Summerside
209
We have a machine with four Kinetix 350 servo drives
Model 2097-V34PR5-LM
We have just replaced our second drive in the last 6 months, and I see that the End of Life for Kinetix 350 is Dec 2022
Suggested replacement from AB is Kinetix 5300 Model 2198-C4015-ERS
PLC is CompactLogix L33ERMS
Anybody see any issues or roadblocks to making the change?
remember on servos, the firmware has to be lock stepped together. Use compatibility matrix on ab to get correct firmware level with new drives. Look for any issues and probably could get the local AB servo/drive guy for assistance.
Since its a known drive configuration i should not blank out your parameters for that axis but be prepared by a backup.
Also would have to go thru a io check/power checks/tuning procedure for the new axis.
I would take screen shots on all the axis screens. off line copy sometimes does not show it. It helps when your trying to tune your drive, because sometimes new equipment is not tight on connections and will give you some out in left field tuning results.
This way you have a way to compare it to a known good tuned parameters. Since your load and torque has not changed just the new drive.
I dont know how many times this saved me from 2nd guessing myself on whether the drive is tuned correctly.
I always seemed you dont tighten the encoder cable all the way, encoder mechanical connection is not tight either on the board or at the encoder, all the other nonsense that you run into with switching a drive out.
Check your panels/sizing etc.
We are also in that boat, & the equivalent drive filter combo is much larger than the K300 we use.
The 2kw unit does not mount onto the filter either, even though the manual states it does.
When we put this back to our distributor, it went around quite a few loops I believe, with end result is they are going to change the manual.
Hello everyone i have a bottle labeler that was working with a Kinetix 300 Servo drive, yesterday rain very strongly, the servo drive dies, the...
1,167
711
Hello, I currently have an Allen-Bradley Kinetix 350 servo drive, 2097-V33PR5-LM and servo motor, MPL-A230P-VJ72AA. What are the correct AB power...
2,415
Hello everyone, any one knows how i can get the Error Code from the kinetix in the Studio?, i was looking on the CIP tags but theres no one that...
1,076
I have a customer with a Kinetix 350 servo drive. They were having issues with the old servo motor so they replaced the servo motor with a new...
18
8,364