I'm almost finished setting up a new system and have a few lingering issues.
The system:
2198-P031 power supply
2 x 2198-D012-ERS3 axis modules
There are two axes connected to the first dual-axis module and one axis connected to the second.
We have a 3-pole contactor feeding the P031 power supply which is currently de-energized. The three axes, according to Logix, are stuck in Pre-Charge, which would appear correct because there is no 3-phase incoming power. Then I energize the contactor, the power supply faults with S23 - AC Phase Loss 2 and the first D012 dual-axis module says INHIBIT S02 - MTR NOT CONFIG 1. The second dual-axis module just remains in pre-charge.
The AC Phase loss seems obvious, so the electricians will check all their wiring, but I keep seeing the MTR NOT CONFIG error and can't find any detailed information. All the motor data was populated in the axis based on the AB catalog number.
The system:
2198-P031 power supply
2 x 2198-D012-ERS3 axis modules
There are two axes connected to the first dual-axis module and one axis connected to the second.
We have a 3-pole contactor feeding the P031 power supply which is currently de-energized. The three axes, according to Logix, are stuck in Pre-Charge, which would appear correct because there is no 3-phase incoming power. Then I energize the contactor, the power supply faults with S23 - AC Phase Loss 2 and the first D012 dual-axis module says INHIBIT S02 - MTR NOT CONFIG 1. The second dual-axis module just remains in pre-charge.
The AC Phase loss seems obvious, so the electricians will check all their wiring, but I keep seeing the MTR NOT CONFIG error and can't find any detailed information. All the motor data was populated in the axis based on the AB catalog number.