Kinetix 6500 problem
Yuri_7811
Jul 2019
Israel
Good morning to all.
After replacing Servo motor in X Axis we get error “Kinetix fault”. (We did it many times without any problems.)
We check problem and found that tag XAXIS.AxisFault return from Kinetix error code 16#0000_0080, also bit XAXIS.AxisHomedStatus is Fail. All drivers “Stopped”.
After module changing we have same problem.
We cant found what means code 16#0000_0080 and how reset it.
Hi Yuri.
It sounds to me like you need to reference your new motor encoder position.
You may need to manually execute the "MAH" in order to get the AxisHomesStatus to go TRUE. This is in the motion direct commands menu.
WARNING: If you do this; ensure you then reference your encoder to the right position- otherwise expect unexpected machine movement and potentially machine damage to occur.
When you have completed this- check in the status that the command has executed successfully..
Regards
Daniel
Daniel thank you very mach for answer.
I tried execute MAH. but get "Execution Error MAH (16#0014). The axis is in the faulted state.
I have connected an incremental encoder with 4000 pulses/rev to the auxiliary feedback connector of a Kinetix6500 module. I want to reference that...
3,335
Dear team, We are constantly facing M07 incremental loss on one of our kinetix 6500 safe torque. We have changed Servo motor (MPL-B4530K-MJ72AA)...
118
Loving AB right now... We have an Allen-Bradley 2094-EN02D-M01 Kinetix 6500 servo drive that once had safe-speed monitoring which was eliminated...
140
Hello, I encountered a problem with the kinetix 6500 drive, error code s22, loss of 3 phase voltage. After disassembling and replacing the thermal...
171
Hi everybody, I am having an intermittent issue with a Kinetix 6500 drive. The fault i get is a SAFE FLT 05, described as GuardFeedback1Fault in...
889