Large wire in panels
Rson
Jun 2017
Michigan
520
We have a panel with a 125HP VFD.
We need to run #3/0 wire from the disconnect to the VFD & line reactor. The normal stuff is hard to bend and we'd like to find a flexible wire solution.
I looked into welding cable, but apparently it isn't usable in a panel where you have to make mechanical connections. Does anyone have experience or insight into this? We don't typically do wire below #1, I just remember from the last job we used #3/0 it was nearly impossible to bend the wires and I'm looking for a better solution this time around.
We have used flexible buss bar in the past.
However, you will still need to follow codes for spacings to the walls for field wired connections. They get pretty large for the larger wire sizes (rightly so)
You should use tri rated cable within panels these are designed for use in panels
BS6231 / UL758 / CSA22.2
These are more flexible than standard cables, make sure you follow the relevant specs on spacing/grouping etc.
Be careful using DLO or other fine strand wire. The lugs on your circuit breakers, disconnects, etc. must be rated for fine stranded wire. They may fail under high current applications.
To crimp the lugs it is essential to have a good cable cutting tool, otherwise the bundle of fine wires will spread out and it will be impossible to enter the hole.
I need some # 2 wire for a section in my control cabinet and don't want to use THHN as it is difficult to work with inside a panel. I have seen...
4,483
Should ferrules be used when connecting large wire to power distribution blocks? Speaking of 4/0 and 500 MCM wire.
2,796
This is more of a power question rather than a PLC specific question but it is part of my PLC panel. I had to upgrade from a small 4A 24VDC power...
30
22,515
I know with larger motors you do not want them to start with a contactor above 30HP or so because they will 'sag' the power in the plant and the...
827
Hello, I'm digging all over the internet to find a solution for this but haven't come up with anything yet. We have 3 nearly identical machines...
968