Latching output issue
turner15429
Apr 2018
Landrum, SC
I'm currently having issues getting an output to latch on and I don't know why i can't get it to work. I'd really appreciate it if someone could help me. The function of the routine I have attached is to check for a abrupt loss or gain in tension every second depending on the tolerance value set on the HMI. I have my logic attached. Let me know if you have any questions.
dLfH47
cQtFrn
gJvjj7
You are comparing your saved values with the window limits. Change them to the live values. E.g. you are using Tension_1_Control in the comparison, use Tension_1 instead.
After looking at it again, I think you have your comparators backwards.
For LEQ to be true, Source A has to be Less than Source B. I would say swap your GEQ and LEQ commands on each latch rung or swap the tags in Source A & B.
Well the reason I did that is because There is some jitter in my load-cell input and if I compare it every second I have a smaller chance of a false reading engaging the E-Stop. The machine test the tension of three separate cables being tightened with a 50 ton and two 25 ton screw jack. I completely broke a cable to test this function and the bit did not latch on.
But you are using the saved values to generate the window values using the offset from the HMI. You then compare to see samed saved values in the comparison. The saved values will never be outside the window values they just generated. In the comparisons you must use the live values.
Yeah originally it was like that but I changed it because I thought it was backwards. I tried it both ways and still no latch. Here is the previous logic
I would say do the original logic like what Bernie said. Compare the live value to the set limits. As far as the jittering load cell, you could use some kind of filter as opposed to the raw value of the input. I deal with much more sensitive load cells than what I think you are talking about and we use a Low Pass Filter inside of our FBD to filter out weird spikes or drops.
Yep you are completely right. Thank you. I cant believe I got hung up on something so simple.
Hi, I am using a pusbutton to latch an output for a solenoid. Another pusbutton is used to unlatch the output. If I latch the ouput then turn...
3,258
I am latching and unlatching "result_Data_latch" bit within same rung. Will This copy/move instruction execute correctly??
195
I am curious why my latches do not work and maybe someone here has some insight. I have created two AOIs. One AOI latches an output on (ON)...
1,798
I'd like to get some feedback on the use of latching/unlatching relays. (Something I've never used in my limited programming experience.) I've...
4,855
I figured out a solution to a vfd issue... at least in theory. Yaskawa has a program called Drive Works EZ that you can have PLC-type functions...
3,858