Logix Tags / Connections
plc noob
Oct 2007
atlanta , georgia
258
When using control/compact logix i see that produced and consumed tags use 1 connection each ( ETHERNET ) to the processor. Which is overloading me on conections.
Now moving this same tag data into a message instruction seems to free up those conections and seems to be about the same speed.
Speaking with AB they say produced/consumed is faster and that tags in message instructions use on connection per tag also.
I have to disagree as this is not what i see.
What is the max amount of dta / tags that can be transfered withone message instruction?
How many connections does a message instruction consume?
Publication 1756-PM0011-EN-P, logix 5000 controllers common procedure (Chapter 11) has the answers for all your questions.
By the way have tried to use an array as a produced tag or consumed, may be this will solve your connection problem.
In my previous reply, the subject, or title said to package the data into arrays. When the message text said see subject, that's what I was referring to. You can and should minimize the number of connections used when using produced/consumed tags by blocking them off into arrays. My statement was that of my opinion that doing this, even when not necessary, is good practice.
I have never setup the udt's in logix.
I do have different data types.
Anyone have any tips on UDT'S?
How many tags per udt? Only one connection per udt?
Are udt's faster or slower than produced consumed?
The message instructions i am using as temp fix seem to only use 1 connection but will this increase if i add more tags to the message instruction.
Are udt's better than the message instruction?
UDTs do not have anything to do with communication, so they are not faster or slower than messages or produced/consumed. UDT stands for User-defined Data Type. You are creating your own type of data, which is a collection of the basic data types, like DINT, STRING, FLOAT, and so on.
UDTs are useful to group related values of different data types. If you have a motor, you might want to know it's speed in RPM, it's temperature, etc. You can create a UDT that contains tags for this information all in a single place instead of creating multiple individual tags.
This website can explain what UDTs are and how they are used pretty well: http://www.plcdev.com/user_defined_data_types_udts_and_oop
Pandersen is right
PLC Noob: Please download same manual as recommended before ( Publication 1756-PM001I-EN-P ) but this time read chapter 2.
Depending on the application, another advantage of Produced tags, is that they can be consumed by multiple clients. I still generally avoid them though, and go with the straight MSG instructions, mainly to avoid having to cross-populate my IO tree with processors.
And you have never used a UDT? They can be just about anything in makeup, and virtually any size. Using a UDT data type in a Produced/Consumed tag or a MSG instruction will send/receive everything contained in the UDT.
You can even include UDT's as members of UDT's (just not recursively).
A Produced tag is limited to 500 bytes of data...
500 SINTs
250 INTs
125 DINTs
62 LINTs
6 STRINGs
??? UDTs - depends on the individual UDT size
I am very familiar with Studio 5000 PLC programming. And I'm very familiar with C-More HMI programming. But this is my first time using a C-More...
317
Hello all. I have a 1769-L16 that I inserted a 1769-L35E into. I was expecting it to create module defined tags automatically in my controller...
1,817
Howdy Everyone, We have an old machine that uses elipse scada for the hmi, and has a slc 5/05 plc,there was a bit getting stuck on from the hmi...
2,006
I know tags can be im/exported from/to an L5K. Wondering if IO tags (Local:1:I) can be overwritten in the same way. For example, if I have an L5K...
781
Hello, I am modifying a program for a 1756-L61 controller using Logix version 20.01. I am trying to add or change datalinks for several of...
1,538