I will soon be installing a sensor whose output is a 0 to 24VDC at a frequency that could be as fast as 500Hz. I would like to connect this sensor to a digital Point I/O input module and, from what I read, it appears I will be ok using a standard 1734-IB8 where the Input Delay Time, ON to OFF is "0.5 ms hardware + (0..65 ms selectable)".
If I calculate correctly, the sensor ON to OF time will be 2ms or longer and so long as I configure my input for 0 or 1 ms, I should be good.
Does anyone see that I am wrong or missing something?
Steve
The problem is the POINTBus polling time and the network adapter connection to the controller. Even at the fastest RPI's available on EtherNet/IP, you're in the 2+ millisecond range, close enough to miss pulses.
Are you trying to count pulses, or perform a rate measurement, or something else ?
The 1734-IK module, VHSC module, or something else might be preferable.
Hey Ken - it's feedback from a flow sensor. From what the Rep is telling us, the frequency should never get quite that high (300Hz is more likely), he suggested 500Hz.
After having taken a look at your suggested 1734-IK, I believe I will order one of those. Better safe than sorry.
Thanks,
Steve
Hey guys, I've recently been asked to review some code at a water treatment plant that isn't working right; seems like sometimes it'll work, but...
5,282
Hi guys, I'm working on a CompactLogix controller and two of my analog inputs are not working. I've triple checked everything and can't figure...
2,178
Hello All, Please direct me to post to the right page. I am really new to PLC, and want to find a tutor who is familiar with Automation Direct's...
471
Hi , Where i can find Mitsubishi PLC Card end of line & replacement model details. i am looking for Q02CPU replacement model. Please advice. thanks
185
I have Allen Bradley plcs, I have had Circuit breakers and other automation equipment in the past. There's no solid buyers local. How much do you...
259