Lost S7cable, ethernet connection ?
userxyz
May 2002
any
2,768
Hello,
I lost my S7 cable (USB to MPI converter).
There is a new cabinet ready to test... but I have no MPI/PROFIBUS...
With TIA Portal and S71200, you can communicate with the CPU over ethernet.
The cabinet to test has a 319 PN/DP CPU. Can I get online (first time connection) when the CPU has not been given any adresses ?
Thanks,
Combo
Yes.
All our projects only have ethenet enabled CPUs.
I dont have any MPI or DP cable.
When you want to download the HW Config the very first time, you must scan for reachable devices. When the scan is finished, the CPU will appear by its MAC address. You will be prompted to set the IP address, and from then on the CPU can be reached by the IP address. I wrote a small guide about this in the downloads section ("How to set the IP adress on a factory fresh CPU").
Thanks Jesper !! This is a big help !!
Yes.
hi everyone, I have a problem, it seems that in somewhere on the programming the reference tends to lost mabye one time at day. I write this...
89
Well, not sure what else we can do with this one at the moment. Will chat with Rockwell in the morning but am not expecting much. Guess I'm...
1,142
When E300 powered off, the ethernet device tag data stayed at last know state, for example, fault bit is still Off, ready bit is still ON, status...
1,041
I'm working with a 1734-AENT PointIO module (manual) connected to a 1769-L30ER controller over fiber ethernet. The 1734 PointIO module has some...
1,062
Hello, My laptop was rebooted lost 500 & 5000 tried to re-install but need to activate, need help badly, Thanks
781