Low Voltage on PLC Card
Bear in mind that when energising contactors or other inductive loads , to close them the current draw is 8 to 10 times the holding current , and if the power supply is not big enough they fail to close properly and draw a higher than normal current . I think your next move is to check the current from each output on the 2nd card , then check the PSU size . It certainly sounds like the PSU is undersized .
It's a 20A PS. It's ran for two years like this, and I don't believe we upgraded any of the motors or the VFD inside it.
How many amps should I see normally from the outputs? It's a 1769-OB16 I believe.
Current per point, max
0.5 A @ 60 °C (140 °F)
1.0 A @ 30 °C (86 °F)
Current per module, max
4.0 A @ 60 °C (140 °F)
8.0 A @ 30 °C (86 °F)
Alright thanks, I'll take a look later.
Are you sure about these values? I would think higher temperature means higher current. Is that temperature the air temp. or the wire temp?
Edit: Sorry, 140°F wouldn't be wire temp haha, so probably air temp.
A 20A supply is more than enough unless you are using 24 V somewhere else as well as the PLC & outputs. Do you have MCB's betwen the PSU and the output cards ? If so , normal MCB's are not usually rated for DC , so check for voltage drops across the MCB's . If they are double pole , check both poles . This could be where the voltage difference between your 0V,s is originating .
Hi All, I have a project at the moment with a Festo PLC to be sent to the states. It must adhere to UL standards which I am not familiar with...
2,372
I have checked a few of the large manufacturers' web pages, but I have a hard time making up my mind about which model to choose. This is the...
8,823
I have a 30 year old Symax PLC. Lately two of the outputs are putting out approx. 8vac continuously without the output being energized. All the...
2,248
I have a analog card 1715-IF16 with six 4-20ma instruments on it. The card in a single-ended method. The instrument has been service for a while...
2,490
Can a low voltage electrical panel be designed to be opened without powering it off first without violating any electrical codes? Panel will...
1,941