Make of plc
Never seen it before but suspect it is a clone of the Mitsubishi FX series there are many versions of them, main differences are limited functionality, 232 rather than 422/485 port.
The LEDs all look they show the status of the X (Inputs?) and Y (Outputs?) with nothing to show whether or not a program is running. That suggests the unit is just an I/O device as others have already pointed out. Follow the cable at the lower right. Most likely it leads to the CPU.
the x and y are seemingly random.... 0-7 10-17, 20-27... but not in order.
30-32.... oops, because we skipped X8,x9, x18,x19, x28,x29 for some reason.... lol
and then they even skipped Y22 for no discernible reason at all... just one random "output" not listed or used, and out of order...
this screams copycat backline 4th shift overnight line running OPS in china.
I am betting that the HMI an integrated PLC/HMI, and the part shown in post #1 is an expansion for this PLC/HMI combo.
Search for Samkoon PLC you will find some images of devices that look similar if not identical.
This is the rear of a Samkoon PLC/HMI
Samkoon-4-3-inch-HMI-PLC-All-in-one-Integrated-controller-HMI-Touch-Screen-Panel-8DI.jpg_Q90.jpg_.webp
Notice the lettering of the terminals are in the same style.
a lot of the samkoon and aliexpress fakes use FX part numbers from real mitsubishi PLCs too. so if you see anything on this that says FX, then I think they're on to something with the samkoon software.
plc
no i/o on hmi so not extension, tried samkoon software no joy,hmi configured for modbus coms so no help
Hello, I want to connect the Factorytalkview ME with rslogix500 to see the live response of HMI buttons in Rslogix500 ladder code . I am using PLC...
47
I have a cell with a compact guardlogix as the plc and I have three hmi's and two vfd's on this cell. I been experiencing momentary comms faults...
95
Hi, hope you doing well I am looking for SIEMENS PLCSIM equivalent in GE FANUC PLC, RX3i PLC thank you
35
Hai, I'm working on Allen Bradely PLC RS Logix 5000 V20 i tried to communicate modbus communication with AB plc and RS 232 to Ethernet converter...
56
Trying to learn PLCs going to start by buying an Arduino Opta Wifi to practice with but what's the PLC I should get next?
270