I have here a proposed network of AS-i..
take a look of my attached file.
Module:
Master and Slave are v2.1
1. Is this network set-up is possible?
2. Do i have to used extra power supply (the BLACK CABLE)
considering that my input are only switches and sensor / and my output are relay and terminal connection of VFD,s?
  • AS-i proposed topology.zip
According to
http://www.ca.pepperl-fuchs.com/pdf/documents/van-115-power-supplies-repeaters.pdf
max combined distance from master to 1st repeater is 100m. If star network (as you have drawn it) is used you have to add 5+95+95+95. So you would be over the max.
Also you have drawn 62 slaves. This would max out the network if they are extended slaves (A and B Slaves) and double the network max if they are non-extended slaves.
I wouldn't advise maxing out any ASi network, especially if you are using it for safety.
I would always use auxillary power for outputs (extra black cable) especially with the number of slaves you are talking about
thanks for the reply....
I'm just curious for the FAQ of as-i on their official site
http://as-interface.net/System/Experts#en-4
Can I install several repeaters in different network-arms?
Yes, in that case it is possible to extend the network up to 500m (Master is located in the middle sector of the network).
How come they arrived at 500 meters?is it a mixed up of EXTENDER and REPEATER?
tnx for the additional reference, the maximum repeater if ur using star topology is 7? based on the manual u gave?
AS-i--Repeater--AS-i--Repeater--AS-i--Master--AS-i--Repeater--AS-i--Repeater--AS-i
I try to illustrate the 500m. You put master on middle, then in both directions at 50m repeater, and then another repeater on after 100m and then you get 100m more. So 2*(50+100+100)=500m.
i will be using s7-300, cpu315-2dp and a cp343-2p...and my slaves will be IFM..
My first plan is to use 2 master that's why i post here if what will be the consideration if i will maximize the technology of AS-i..
thank you very much to all of you for all the response and it is very appreciated...
another question:
1.can you give me some computation and consideration when will i used the black cable?(the additional voltage)
2.I want this one to be clear also...i will used as-i power supply after the repeater and an ordinary power supply 24vdc for extra supply the black cable. Am i right?
tnx
I use the Black cable based on whether I need it for the Slaves. For your lengths for sure. Step7 handles the AS-I stuff well.
For what it's worth I have seen a lot of problems with IFM slaves. I'm picky that way if I get burnt once I stay away.
Check this out...it's good. http://support.automation.siemens.com/WW/view/en/40737628
another question:
tnx
Well i did not suggest using 500m, i just told how its possible. I would not do it. Not worth to save few hundred on not buying second master(or dual master), then have plant down becouse of that.. And lose many times more.
After much reading help documentation and forums for Codesys, I have run out of ideas and once again try the forum which has provided much...
2,699
Good day: I am wondering if anyone has experience with the Kinetix 5500 S33 Fault. I have 3 drives in a group set as follows: 2198-H025-ERS2...
41
Hello, I have a motor that we are sending a RPM Speed Output from 0-100% to the VFD. However, the Motor HP needs to be limited to 6000 HP and the...
101
Hello, I have a quick question. I have been using scripts to change the color of buttons. The reason, I am usually using multiple hmiruntime.tags...
121
Good evening all! I hope you folks are doing alright today, as I've got a situation that I believe I've come up with a solution to but I wanted to...
457