Micro 820 - 2080-TC2 thermocouple filtering
RMore
Dec 2011
Kenmore, NY
64
What's the most effective filter to use for the thermocouple wiring on the input to the 2080-TC2 plugin module on a Micro800 based design?
Additional information: The 2080-TC2 module is intermittently faulting a few times a day, potentially due to a solenoid switching. Most of the time the fault only results in a bad reading or two, however, on a few occasions it has crashed the program resulting in error code F0A1h). I assume that it is noise from one of the solenoids making it's way to the TC module, either thru the power supply or the unshielded TC cable, however, I am not yet able to get it to fail on the bench. Has anyone experienced faults on the TC Module and what was the ultimate fix?
https://www.youtube.com/watch?v=8KhqIbwcOhg
http://www.mosaic-industries.com/embedded-systems/microcontroller-projects/temperature-measurement/thermocouple/thermocouple-noise-filter
Dirt, Thanks for the replay. Useful information ,however I do not have control over the input circuit design for the module and Rockwell does not provide a schematic. Also, the module does not provide a ground terminal. I was able to determine that the input impedance is roughly 340K with the negative input tied to ground thru a 10K impedance.
Currently my update rate is 16.7Hz I can change it to 50Hz. Can you explain what factors determine the optimum update rate?
According to the manual 16.7 Hz refresh rate will result in an accuracy of + or - 1% (Do you really need that tight of results?)
A 50Hz refresh rate will result in a + or - 3% accuracy (This forgives a lot of noise/spikes/Etc..)
You might just try and make sure it works for your needs.
What about ferrites?
Has anyone had any success using ferrites on thermocouple wires to reduce noise spikes getting into the inputs? What about adding a cap or MOV across the input?
Surge protection on all inductive loads? Will help if this is your problem.
MICRO 820 PLC - 2080 MOT HSC - Jencoder J-15S-SL Above plc, add on module and encoder are using to configure one paper cutting machine...The...
3,898
I’m running a micro 820 to measure a tank level, then turning on equipment at certain levels. I have an analog input (4-20) that I’m storing and...
302
Hi All, I came up with this for ramping the PWM pin on the micro 820. I'm new to ladder logic so I am not sure if this will even work? Once...
375
The micro 820 is visible in RS Who when I configure my Ethernet to capture the random IP. I am getting an error when following the steps below...
1,005