micrologix 1200 C series Modbus configs
rudan206
Oct 2013
Rabaul
I've got a ML 1200 C series with only 1 port and would like to connect to our DCS via Modbus. Since there's only one port, I've decided to employ a 1761-NET-AIC+ to provide for extra ports for Modbus and programming. Problem now is how to get PLC configured for Modbus. I can change the channel from DF1 Full Duplex to Modbus RTU Slave but then I won't have any port for programming.
Welcome to the PLCTalk forum community !
You have identified the basic issue: the controller has just one port and can only be configured for one protocol at a time. You cannot simultaneously go online to monitor the controller and have it connected to the DCS via Modbus.
The "R" version of the MicroLogix 1200 with a second serial port, or the Ethernet-equipped MicroLogix 1100 or 1400 controllers would be required for that functionality.
If you can tolerate using the DCOMM button to switch to DF1 Full Duplex when you need to download or monitor, then you can make use of this controller.
Hi everyone, I have been trying to work on an issue in AB MicroLogix Series C with an analog module IF4 for quite some time now, but now am...
4,557
Hi everyone, I'm working on a project where I need to exchange data between a Siemens S7-1200 PLC and an Allen-Bradley MicroLogix 1400 PLC. The...
654
I have a MicroLogix 1200 that has an 8 input and a 16 output. Every 6 months-year I get a fault and when online go to error it is something like...
510
Have a bad output on a Micrologix 1200. Moved wire over to an available output, changed program to associate with new output. downloaded program...
755
I need help achieving the following task: ML1200 sending 4 to 20 mA thru analog output ch0 to a DC speed controller analog input(4 to 20 mA) my...
673