Micrologix 1769-l24er (Code 16#0022)
1s_and_0s
Aug 2018
Dalton
**Compactlogix** The fault that I am getting is; (Code 16#0022) an invalid reply was received. Reply service code does not match the requested service. The embedded analog I/O and HSC is not being recognized. I have checked the end link, downloaded a different firmware version, checked my 24VDC power supply feeding the plc, and changed the RPI. I am not sure what else to try.
Yeah, I have micrologix on my mind because I am programming one right now. It is a Compactlogix. Unfortunately the company that I am at will not allow me to send the program. I have this same program loaded on another plc and it is working fine. I will double check the terminal board.
This is undoubtedly a 1769-L24ER-QBFC1B CompactLogix 5370 controller with embedded digital/analog I/O and HSC.
widelto said:
I made a mistake, you said embedded. My apologies.
As the L2 CompactLogix controllers support 1769 modules, this controller still requires a properly fitted 1769 End Cap Right (1769-ECR), even when you are only uses the embedded I/O. So you have not made any mistake here Widelto (I read your original reply before edit).
Yes 1s_and_0s, please re-check the "end link" if that is what you are calling the End Cap?
The embedded I/O module instances are automatically created under the I/O Configuration when the project is first created. So unless that has been messed around with or has become corrupted, it is usually the End Cap that is not fitted correctly. Plus it's the easiest thing to check first (even though you've jumped a few hurdles already).
Regards,
George
Using Rslogix 5000 Data Access manual as a reference I keep getting 'Service Not Supported' response when using symbol instance addressing to...
1,569
Hi guys, I have taken on a project to migrate a ML1500 project to a CompactLogix L36ERM. I have tried using the RSLogix Project Migrator and...
3,399
Hi, I am Akash. I am currently working on a PLC upgrade project from micrologix 1500 type to compactlogix 1769LRP. I have migrated the whole...
5,439
Good Morning , I have a MicroLogix 1500 program I would like to convert to a CompactLogix 1769-L18ER. Can I use the RS Logix 5000 Tools/...
4,032
Hello All, I have a total of (8) prox switches that I am monitoring (1 for each machine) with a single MicroLogix 1100 controller. I have (8)...
5,257