Migration to PV+6 1250 With 2711P-RN6 DH+ Network

ctsoft

Member
Join Date
Jan 2007
Location
singapore
Posts
26
Good day to all.

Existing plant have 7 x PLC5 system on DH+ network and 7 x PV900RIO talke

to respective PLC. There are 5~6 screens per PV900RIO.

I'm planning phase out all the PV900RIO and migrate all the screens into

one PV+6 1250 with 2711P-RN6 (DH+).

like to know that is 2711P-RN6 capable communicate with these 7 x PLC5?

Hope someone can share the knowledge and things to beware when doing

this migration.

Thank you.
 
In my personal opinion, you might have to spend a lot more time and a little more money to set up a gateway (Controllogix rack with DH+ and EN2T) and use Ethernet for all new HMI communications. The gateway rack can handle the bridge between DH+ and ethernet for multiple nodes on the DH+ network. That would allow you to move forward with non-obsolete HMIs using ethernet communications and gradually phase out segments of the DH+ network.

The main reason I would recommend this is that I believe the 2711P-RN6 is obsolete, and I am not a fan of new installations including obsolete parts when it can be avoided.
 

Similar Topics

So basically i have 2 queries : 1. I have a program file of S7-300 PLC which i want to migrate in RSLogix500.In short i want to convert my simatic...
Replies
10
Views
82
Hi everyone, i have a Siemens S7-300 Cpu 314C-2 DP with several cards of i/o and servos my laptop has TIA version 16 and 17 loaded and...
Replies
4
Views
168
Good day, May I ask, what do I need to perform MIGRATION of HMI program from Siemens MP277 10" Touch hmi to TP1200. I already have WinCC Flexible...
Replies
0
Views
164
Existing environment shown in attached photo (Existing.jpeg) Proposed Environment shown in attached photo (New.jpeg) I am migrating a PLC5 system...
Replies
0
Views
596
Hi All, We have a number of old discontinued 1756-L1 PLC systems that we are trying to support but recognize that we need to start preparing to...
Replies
5
Views
981
Back
Top Bottom