Mitsubishi Digital to Analog Module
BigAl
Nov 2002
Syracuse
38
I have just started working for a new employer, who has purchased several used machines at an auction. Each unit has a Mitsubishi FX-32MT PLC with an FX-2DA Digital to Analog module attached to it. Unfortunately the program has been erased from the PLC, and the original manufacturer is no longer in buisness. I have GX developer on my laptop, and have no problems connecting with the PLC, and starting a new program. My only draw back is with the FX-2DA module. I understand that it is a digital to analog convertor, but when I asked Mitsubishi for a copy of the manual, they informed me that this module is obsolete, and that I should ask my local distributor. My local distributor is clueless.
Does anyone have experience setting up this module? I would appreciate any help.
Big Al
FX2ADPT User Manual
Hi Big Al,
The UK Mitsubishi site is being reconstructed, try the USA site at http://www.meau.com
Look under Documentation Downloads
Industrial Automation
PLC
PLC-F (Search)
The Manual is JY992D28501-C
Regards,
Gene
FX2N-2DA Manual
Sorry Big Al,
The above was incorrect.(My fault for not checking properly)
Try this link instead.
http://www.syslink.com.cn/downloads/manuals/FX2N-2DA.pdf
I can't find a refrence for the original FX version, but this looks similar enough to get you underway.
I'll see if I can get the exact refrence manual your after, a.s.a.p.
What's the application, what are you looking to control via the analogue output ?
Regards,
Gene.
Thank you Gene.
I initially downloaded the manual for the FX2N-2DA module, thinking that the modules would be pretty similar. I used the program example shown in that document, and was still unable to get the FX-2DA module to respond.
The modules I am dealing with are used to send a 4-20MA signal to a Dynatronix rectifier. The machines they are installed, on are used for electroplating. The rectifier is supposed to provide very little current at first, and gradually increase it over a specified time period.
Thanks again,
Big Al
FX-2DA Module
Hi Al,
No chance with a .pdf file, apparently one doesn't exist.
(Please check your site mail here)
The code will still be similar to the FX2N-2DA version in terms of TO and FROM commands, but these are the Buffer Memory addresses for the FX-2DA.
BFM No.
#0 Analogue o/p mode (current / voltage) default = (H00)
#1 O/P CH1
#2 O/P CH2
#5 Last Data Reset default = H00
#3,4,6 - 19 Reserved.
The value of BFM #0 switches the analogue o/p between voltage / current.
The value of BFM takes on the form of 2-character HEX number. The least significant character controls CH 1 and the other CH2.
H00
0 = 0 Voltage o/p (-10V to +10V)
0 = 1 Current o/p (+4mA to +20mA)
Hence H10 CH2 I CH1 V-------------------M8002
-------H11 CH2 I CH1 I--(Your requirement -||------TO K0 K0 H11 K1)
------------------------------------------Init Pls
BFM #1 CH1 data (default = 0)
----#2 CH2 data (default = 0)
BFM #5 Output status regarding PLC mode. If the PLC is changed to the Stop state, the FX-2DA will continue to output the last value.
To reset the output to the offset value, set the HEX characters of #5 to one of the following settings.
H00 CH2 = Hold CH1 = Hold
H01 CH2 = Hold CH1 = Offset
H10 CH2 = Offset CH1 = Hold
H11 CH2 = Offset CH1 = Offset
BFM No-------------------------------------b3 b2 b1 b0
#20 Reset all to default default value: 0
#21 Gain/Offset adjust prohibit--------------------Prohbt Permit
(Initial value (0,1)
#22 Gain/Offset setting command------------G2 O2 G1 O1
#23 Offset Data (in mV or yA units) default value 0
#24 Gain data (in mV or yA units) default value 5000
#25 - #28 Reserved
#29 Error Status
#30 Identification Code K3010
#31 Reserved
Regards, Gene
I need to add a QX10 module to our PLC because we've run out of DI channels. Does this module need to be configured in a similar way to the...
2,222
Hi, I need to send a digital output to turn a water pump Inverter driver ON/OFF. To this end, I'm planning to use a Digital Output Module, i.e. it...
3,550
Hi Guys, I have five different bits which I want to set up in Alarm display. But I'm lost on the alarm set up even with the manual. Please, I...
1,813
Hello! If someone can help me with the following problem. I can't change the phone number. Do I really need the interface (AL-232CAB - Programming...
52
how to communicate FactoryTalk Optix and Mitsubishi Q Series. I want to know the details of that
49