I have a fx1n 40mt and I am runing the Gx developer Fx ver.5 , I have a program that I know works that I loaded into the plc .The plc is in run mode
however I have no output , when I moniter online the rung that I am controling through a screen shows all the conditions to get the output however the coil wil not output. it can be forced on through the plc . so I know my common for the outputs are ok ,and the inputs show up on the plc as well as in the ladder rung.
never seen this before , I changed plc and the same result .the plc is in run mode . I know its has to be something simple that I have over looked any help or ideas would be grand .
Could it be that you have the code inside of a nest? If the MC coil for that nest is not energized, when you monitor the code, you will see exactly what you are describing...
Another possibility would be the use of a true ZRST function-- the output could be coming on, but be reset at the next scan...
Post your code/program, and you may get some better help.
It may be one of the following:
- The rung is not executed, being within STL or subroutine or bypassed by jump.
If you can force the output on/off and it maintains this status, this is your case.
- Double coil: the rung output device is being controlled somewhere else in the program.
- The rung condition(s) are not really true. Rememeber that you are monitoring the devices status as it is at the end of the scan, not during this rung execution.
- Also, some of the conditions may be false for so short time that you simply cannot monitor this.
- And finally, be sure that the program in the PLC matches the program in your PC.
Thanks for the help
I found the problem the following morning . I had forced a bit to trouble shoot a new machine this set another bit in the program and prevented it from runing .
thanks for your help
Hi guys, Im trying to set the real time clock in my Mitsubishi FX1N, but it shows this error ES: 01800001 I have good communication with...
172
Hello people, i'm new with the mitsubishi FX1n-24MT plc and with the gx developer its very new to me and i want to implement for students a stand...
928
Hi, Does any one know how to communicate MItsubishi FX1N or FX2N with or without 485/422bd with Pro-Face GP2300 HMI?? I tried to summon Hades...
2,250
Hi guys, I've encountered a weird problem backing up my old FX1N-24MR-ES/UL PLCs. Hope I can get some helps here. I'm grateful for all the help...
1,886
Hi, I am working on the project that needs to communicate with FX1N PLC by serial port protocol from PC. I am using USB-SC09-FX cable to connect...
2,732