Modbus for S7 300
teh
Supporting Member
Nov 2002
140
I going to using modbus for Communication with third party..
But I can't look for Modbus module at siemens sales catalog.
How should i do it?
look for the additional convertor? ( TCPIP to Modbus )??
Rgds
I'm not sure if this is what you're after
I'm using the 341-1CH01-OAEO serial communication module to communicate modbus RTU with some GE Multilin 369 units and some Yokagowa UT-550 controllers.
In addition to the module, you'll have to purchase the modbus driver.
Hello, teh;
When purchasing the Modbus driver for the CP340/CP341, make sure you know whether you will be Modbus master or slave; there are 2 different drivers in the Siemens catalog.
Once you have the driver installed, use the example project that comes in the documentation for the CP340/CP341 (you can download it from the Siemens webpage) to establish a basic communication link; then modify it to suit your needs. It is the easiest way to make sure all functionnalities are available to you.
Hope this helps,
Daniel Chartier
119
there is status 16#7000 for modbus master block and there is no data appear when make communication between plc s7-300 and generator deap see...
1,204
I was updating my FIU (Master?) to try and improve radio communications. But I also ended up deleting the Modbus configuration on Port 2, so my...
1,476
Hi, I would like to test my program according this manual...
2,213
Hi, I got two questios: There are two slave devices(SEL-787) from which I should read data via MODBUS RTU. I checked SEL-787 manual and it says...
5,569