Modbus Master-Slave
gibson
Sep 2012
mumbai
46
Hi all,
I am using ML 1200 (1762L24BXBR) to communicate with Industrial PC Serially with Modbus using 1762-cbl-pm02. Here, Industrial PC is acting as Modbus RTU master and PLC acting as Modbus RTU master. Now i want to add another Industrial PC in current system which will be acts as Another modbus Master device.
Since their is only ONE communication port available on ML1200 so what changes do i need to make in my current system..? Can i use Port splitter ?
Note: Prog/HMI has been utilized by ENI utility module which is then directly connected to Industrial PC.
Modbus can only support 1 master on the network at a time. The issue with a port splitter is that both master A and master B may try to send a message to the slave at the same time. Or worse, master B may send a message while the slave is responding to master A.
ProSoft makes a module that allows you to connect up to 3 Modbus master devices to a single Modbus slave device:
http://www.prosoft-technology.com/Products/Gateways/Modbus-Master-Slave/Modbus-Serial-Port-Expander
The module listens on each of the 3 ports and when a Message matches the node ID in the configuration file it forwards it to the slave device. If while sending this message to the slave device another message comes in, it is placed in the buffer, and stored till communications with the other master device has been completed.
This would allow you to have 2 masters talking to the same slave.
Does anyone have an example project of the cm ptp ET200 SP HA with 410-5H DCS (PCs7 9.1 SP1) for MODBUS MASTER/SLAVE communication ?
138
Hello, I am quite new to PLC programming. The master would be a Beijier HMI (iX T12B SC) and the slave a Beijier Nexto (XP340). I have...
3,265
I successfully got a Micro 820 (Slave) and Red Lion HMI (Master) to work together using Modbus TCP. But now I need to add an Automation Direct...
2,673
Hi, I need to read from my PLC which is Modbus TCP/IP Master one Siemens S7-1200 PLC which is configured as Profinet IO Device. I know what are...
3,179
Hi All, I'm seeing Point To Point for S7-400 Master/Slave Modbus RTU connection. How can I do RS485 multidrop using CP 441-2 and Modbus driver...
1,309