modbus rtu maximum length of cable

what is the maximum length of cable can modbus rtu go? do you have any curve showing cable distance versus baudrate?

Google is your friend:

https://www.maximintegrated.com/en/app-notes/index.mvp/id/3884

and from Wikipedia:

Since it uses a differential balanced line over twisted pair (like RS-422), it can span relatively large distances up to 1,200 m (4,000 ft). A rule of thumb is that the speed in bit/s multiplied by the length in meters should not exceed 108. Thus a 50 meter cable should not signal faster than 2 Mbit/s.
 
what is the maximum length of cable can modbus rtu go? do you have any curve showing cable distance versus baudrate?


RS232 or RS485/RS422?

RS232 = 50ft (I have seen as much as 150ft at 9600 baud rate, good cabling)

RS485/RS422 see tragically1969's post.
 
Predicated on using low capacitance comm cable:

Distance_vs_baud-rate_B_and_B.jpg
 

Similar Topics

Dear All, i am trying to connect Danfoss inverter with s7 200 cpu 226.but microwin shows following error at DATA Ptr.i assigned different VB...
Replies
1
Views
51
I'm trying to control a device via MODBUS RTU and the ModbusRtuMasterV2_PcCOM in Twincat 3. I've configured a device with the right com port and...
Replies
7
Views
226
Hi all, Currently having trouble getting a speed reference to write over modbus to an Omron M1... I can successfully write a run command and...
Replies
6
Views
264
Hi, I'm having an issue with a mircologix not transmitting out. The current setup is a mircologix 1400 connected to a Guardian 100 Radio...
Replies
1
Views
116
If a device has Modbus RTU over serial and Modbus RTO over TCP and Modbus TCP then there is a difference between Modbus RTU over TCP vs Modbus TCP...