137
Wizards,
I hope everyone survived the storms the last few weeks.
After everything calmed down here in Oklahoma, I was farmed out to get this Signal-fire wireless telemetry system working.
This project was started in 2016 and abandoned shortly after.
I have managed to get the signal fire things to work, and located a RTA 460ETCMC Modbus master to transfer data from the Modbus slave to the control logix plc.
Useful information:
Slave Register data:
Type-Pressure Scout
Name-System_9
Slave ID- 109
Node Address- 45569
I need to monitor the Pressure and the Battery alarm
Pressure is Data type 16bit UINIT
Pressure Register Address is 3001
Low battery alarm is
Register address 65523
In the end, there will be 30+ different slave devices with unique ID, Name and Node Address.
Batteries are dead in most of them, so I will not be able to configure them all, but I do have 3 that are functional. (have to shut down the paint system to change batteries, so they wont be working until after this weekend shutdown. The whole, blow up the building from sparks thing...)
Thanks in advance,
Gad.
You'll have to check the slave documentation to see whether the values are in holding registers at (4)xxxxx or Input Registers at (3)xxxxx because the command that the master issues depends on which type of register in which the slave holds the data
could be
pressure at (4)003001 or (3)003001
low battery alarm at (4)65523 or (3)65523 (most likely a Holding register because a battery alarm is not an input)
register values like you've given are most like one-based, not zero based register addresses.
Looking for a modbus reference for a comap IG-NT GC HW version 1.3. Any help would be appreciated.
1,568
Hi everyone, I am working with 3 Franklin Electric P Series drives. I am communicating with the drives via Modbus 485 with a MVI69E-MBS Prosoft...
1,550
Is this possible? I want to read values from a power meter directly into my PLC. Is there any kind of documentation on how to set this up? My CPU...
6,364
OK Gang, I'm setting up a M340 system using Wonderware as the HMI and I really want my DASMB server to match the addressing in the PLC and not be...
2,199
Hello, I am setting up Modbus Server by using MVI56E-MNETR and i am confusing on offset parameter and don't know how to set. Client want to...
2,675