Modicon Quantum (Unity) To ABB ACS 550 Drive
MadPLC
Nov 2009
Delta, BC
47
Hello all, first time poster here.
I have a Quantum PLC and am trying to connect to an ABB ACS 550 Drive. We are using Modbus TCP with a RETA-01 module on the drive. The communication link is ok as the RETA module sees the network but we can't get the PLC to talk to it.
We have tried all the variations of address in setting up the PLC I/O scanner (1, 40001, etc) but nothing. I have gone through the parameters and set them up according to the literature available. There is no joy in MudVille today.
I am open to pretty much any idea at this point as we are trying to start up a new plant and this is a huge hurdle we need to overcome. ABB tech support was helpful but still nothing.
Thanks everyone.
Go back to ABB Tech Service and insist on speaking with a Fieldbus specialist. The Tech service guys are generally very good but Fieldbus is enough of a specialty that you need one that focuses on it.
Well I was able to control the drive with a message command from the PLC. You have to set up a message block to read and write. All I am waiting for now is word back from ABB if the drive can acept a permanent TCP connection. The message block is an open and close type connection whereas the I/O scanning of the Quantum needs a permanent open connection. I don't know if the drive supports that and if it does how do I set it up.
If ABB drive supports Modbus TCP, it can act as Modbus slave and Quantum PLC can use I/O Scan to control the drive.
I guess, you must have done the I/O Scanning configuration under the ethernet link ( either base CPU module or NOE module ) in Quantum. Remember that all modicon addressing starts with 1 ( and not 0 ) and hence there may be an offset of 1 in your register addressing.
ABB 550 Modbus Protocol has addresses with digit 4 as prefix. While communicating with ABB AC31 PLC, the function block in PLC has Address tag as a WORD input which cannot be greater than 32768. Whereas ABB 550 has Address of 40000 onwards. Please suggest.
hi all i have a problem with Modicon Quantum PLC i have hot standby CPU 140 CPU 671 60 , it was work perfectly while doing routine check for CPU...
5,666
Is it possible to program a Quantum Unity CPU with Concept software? Do exist a flash executive that makes it possible? Regards, Robert
5,259
Hello All, Was hoping I could get a little help with Modicon ladder logic. This is the first time I have seen Modicon logic and currently trying...
315
Hi There, I have a Modicon Quantum PLC, there is a alarm on display "noConfig" its happened after power failure, I have gone through manuals...
674
When i read the specification of 140CPU43412A i observe that as remembered in specification 1. Local i/o : Maximum i/p and o/p words are 64 in...
507