module status over EthernetIP with PLC5
Jean-Luc
Aug 2011
Curitiba
39
Hello,
I have to control a RFID module with an enhanced PLC5, by EthernetIP. To do that, I will add an 1785-ENET card in the PLC's rack, using channel 3.
For the same module with ControlLogix, It's possible to get the connection status by an GSV instruction with an attribute EntryStatus. Do you know if exists an equivalent way to get this information with a PLC5 controller ?
Thanks for any response
The PLC-5E and 1785-ENET module do not have the same I/O scanning or EtherNet/IP messaging features as the ControlLogix has.
Because there is no I/O connection, there is no equivalent connection status object. Typically devices that use MSG instructions rely on the /DN and /ER bits of the MSG instruction to determine the network status of the device.
You need to consult carefully with the RFID device maker to find out if their device is compatible with a PLC-5's Ethernet messaging capabilities.
Thank you Eddie,
According to the documentation of manufacturer, the module can work with PLC-5 ethernet messages (depend of series). It can write/read the I/O by messages (PLC5 typed write and typed read) with "IO" target. I just hoped it was possible to do the same with the connection's status using an equivalent message fof GSV/EntryStatus.
So, I will test the .ER bits of the MSG to check the connection.
Hello All, Can you check the below configuration and tell me how to check the module status of modules in the secondary rack of a redundancy...
502
Hello, I have a question regarding the status checking of the module in the secondary chassis in a redundancy setup. CHASSIS 1 ...
1,151
Hi Folks, We have this M580's configured as hotstandby and is curious if it is possible to monitor the modules on the remote racks. Unity pro...
1,597
Hello all, We had a problem with 1734- Digital input module. The module was damaged because of some short circuit with the Input. We replaced...
1,476
Hi, I am using the GSV(Module, [Module], EntryStatus, [Dest]) instruction to check the status of an IO module. It is packaged up nicely in an...
1,577