I am suspecting that one of our slc 5/05's is losing power intermittently. Is there anyway to moinitor or count when this happens? I looked in the S2 file and the is a fault/powerdown section
Rung# S:20 = 0
File# S:21 = 2
Is this saying i had a power failure? If not, how can i monitor it. Right now i am leaving a pc online with the plc and hoping that i get a communication error if it loses power for a second.
It sounds like you are looking for a software way to do this but a simple hardware way is to hook up a relay to the power supply.
Get a relay that you can manually operate. Wire a normally open contact in series with the coil and then manually activate the relay.
If the power flickers your relay will drop out and not reset.
From the help
Fault/Powerdown (Rung #) S:20 - (File #) S:21
This is the word and file that the processor last executed before a major error or powerdown occurred.
RSLogix 500 - Copyright Rockwell Software 2000, 2001, 2002
You could program a user fault routine
Startup Protection Fault S:1/9
When this bit is set and power is cycled while the controller is in the REM Run mode, the controller executes the user fault routine prior to the execution of the first scan of your program.
You could every minute of so copy the time and date to a set of registers and then if the power fails and comes back up then using the User Fault Routine copy the last recorded time and date stamp into a different set of registers (perhaps with indexed addressing etc). This will then give you a record of the last X power failures with time and date stamps.
If it is in run mode, at power up; I would think that you could use the first pass bit and a counter, or as Dave said, log the time and date into files if you need that info. The relay thing works well also.
Is your program resetting, or what is causing you to think there is a power failure?
brian
well supposedly earlier today, all valves and pumps that are controlled by that plc spontaneously closed/shut off. They say it happened twice and they immediately went to the hmi and were able to restart all of it.
If N7:0 is any number other than 0 or 1 (it will initialize to one the first time it runs after you install it unless you program it in online in which case it will be 0) then you will know that power has cycled. I think you will want to use an add statement rather than a Counter becasue the prescan sets the counter CU bit so that a counter counts on transiton, not on rung state on the first scan. (I'm not 100% sure on that, but if I recall correctly that is the case)
Hi. I’m looking to replace a basic Shark power monitor with a newer one with communication options, probably PowerMonitor 5000. The existing one...
998
Can anybody help out with this...somebody has sent me the ZIP for the PowerMonitor_AOI_FP_1.1 and asked me to import it into a PLC program I'm...
1,148
I'm looking for recommendations on 3-phase power monitors with Modbus TCP protocol. I've been using a Socomec Diris A10 to monitor 3-phase...
4,321
At my wits end.....I have a Siemens S7-1200 and a Sentron PAC3220 Power Monitor. Got the MB_Client command to connect and work in TIA 15.1 but I...
1,623
good morning all I have several red lion da30d using crimson 3.0 on the controls network in the plant. I am thinking about getting the AB power...
2,169