Moxa converters
mikecqm
May 2003
italy
I am looking for documentations concerning the multidrop connection between rs 232 plc.
I am used to connect them (2 or more) by a "MOXA converter A50-A52", but I have often problems with the new version (A52).
The problem is that the Cx, sometimes give me a connection error while I am online with 2 or more Plc';
My test configuration is made :
pc (cx)--moxa(1)---------moxa(2)----------moxa(3)
moxa 2 is connected to a Rs232 Cqm1h
moxa 3 is connected to a Rs232 Cqm1h
The connection between the moxa is done RS422 (4 wires), and also tested as RS485 (2 wires).
I did it without problems by A50 model, but with the same network configuration seems to be impossible to have the same rusults....
If somebody has some suggestions.....
Mike
Yes, it is possible to use RS422 and monitor multiple Omron PLCs. I suspect that the Automatic Data Detect circuit is not reliable. I suggest that you use hardware control (RTS) to switch the transceiver. Here are some modified cuts out of the A52 manual. The pinouts for the cable are for Omron 9Pin serial port.
Hi All, I have set up a Moxa NPort serial server for an application. Unfortunately the environment requires NAT forwarding between 2 systems...
836
We've been using Allen-Bradley's 1783-NATR and find it is easy enough to work with. Unfortunately, it only allows 5 ports to be opened per IP...
792
Dear all When I am using Moxa Mgate 5105 convertor for converting Modbus TCP IP to Modbus serial RS 485 I am getting swapped word as LSB and MSB...
1,408
Hello. I'm considering using DIN rail mounted, managed Gigabit Ethernet switches from Moxa...
20
4,997
Hej Guys. Is anyone that has knowledge about setting up communication via ethernet from Keepware OPC server to MOXA NPORT? the keepserver keep...
2,027