I've got a situation where it would be advantageous to have 2 PVs hooked into 1 PLC (SLC 5/04). The PVs I have are 2711-K5A5 which say they are DH-485. I'm unsure if its just a straight networking of them node to node to node, or do I require NET-AIC's on each node. I haven't yet been able to find any docs on the AB website concerning this setup with these part numbers. Any help would be appreciated.
 
Your SLC5/04' serial port will have to be configured for DH485. Then connect it to a 1761-NET-AIC. Your PV's have a RS232 port with DH485 protocol. You will need a 1761-NET-AIC for each PV.

See link to the manual below. Chapter 12 has info on hardware and cables needed.

http://literature.rockwellautomation.com/idc/groups/literature/documents/um/2711-um014_-en-p.pdf

Below is a link to the 1761-NET-AIC manual

http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1761-um004_-en-p.pdf
 
two PanelViews 550'son one Controller

I just did four machines that each had 2 PanelView 600's connected to a Micrologix 1500 via DH485. They all worked excellent. As stated above just use the 1761-NET-AIC module and make sure you give PanelView one a node address of 2 and PanelView two a node address of 3. I my case the Micrologix was node 1.
 

Similar Topics

Hello, Anyone have a nice working solution they can share where there are a handful of engineers that work on one project. I have setup 2 SEL...
Replies
7
Views
130
Can I connect two A-B Panel View 7 to a A-B PLC. Same graphics etc. One on the local control panel and the other Panel View 7 in a remote control...
Replies
2
Views
72
is it possible to install multiple ibaPDAs on single VM or PC?
Replies
0
Views
47
Hi. I need to create several alarm servers in an application, but first I need to know if there is any impact on communication, or if more...
Replies
0
Views
89
Back
Top Bottom